Hello all. I am trying to get 125 amps 3 phase back to a paintball field to power an electric air compressor.

I have a 3 phase 120/240v PG and E feed, 200A panel about 1300' feet away from the desired location. I have 2 transformers, so we can transform up to 480 to make the 1300' run, and then transform it back down. My question is what size aluminum wire do I need to get the job done.

Please excuse me if I mis-used any terms, this is pretty new to me.

Thank you
 
Hello all. I am trying to get 125 amps 3 phase back to a paintball field to power an electric air compressor.

I have a 3 phase 120/240v PG and E feed, 200A panel about 1300' feet away from the desired location. I have 2 transformers, so we can transform up to 480 to make the 1300' run, and then transform it back down. My question is what size aluminum wire do I need to get the job done.

Please excuse me if I mis-used any terms, this is pretty new to me.

Thank you
1300 feet is a long way and I don’t use aluminum but I would have to say 200 MCM which is the next size wire to 4/0. You will waste a lot of money on transformers. You shouldn’t have any problems
 
Wouldn't it be better to use a compressor with a diesel engine?
 
  • Like
Reactions: Megawatt and James
Or even a pipe to carry the air instead of a wire for electricity?
 
Looks like the OP hasn't been back since.
 
  • Like
Reactions: Megawatt
Looks like the OP hasn't been back since.
Probably because of the price of wire. 1300 feet for a neutral, 2 hots and an equipment ground. That’s 5200 feet of wire. Not cheap
 
  • Agree
  • Like
Reactions: nicebutdim and DPG
Probably because of the price of wire. 1300 feet for a neutral, 2 hots and an equipment ground. That’s 5200 feet of wire. Not cheap
A standard mile of cable!
 
  • Like
Reactions: Megawatt and DPG
Wouldn't it be better to use a compressor with a diesel engine?

Yes, much better/cheaper to use an engine driven compressor, or even a generator and compressor. Especially considering how much cheaper fuel is over there than it is here.

Or even a pipe to carry the air instead of a wire for electricity?

That would be a very large pipe to compensate for the pressure loss, this works much tbe same way voltage drop does.
 
  • Like
Reactions: nicebutdim

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
3 phase run of 1300 feet
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
Davis PB,
Last reply from
brianmoooore,
Replies
8
Views
1,554

Advert