Davis PB
Hello all. I am trying to get 125 amps 3 phase back to a paintball field to power an electric air compressor.
I have a 3 phase 120/240v PG and E feed, 200A panel about 1300' feet away from the desired location. I have 2 transformers, so we can transform up to 480 to make the 1300' run, and then transform it back down. My question is what size aluminum wire do I need to get the job done.
Please excuse me if I mis-used any terms, this is pretty new to me.
Thank you
Thank you
1300 feet is a long way and I don’t use aluminum but I would have to say 200 MCM which is the next size wire to 4/0. You will waste a lot of money on transformers. You shouldn’t have any problems
Wouldn't it be better to use a compressor with a diesel engine?
Reactions: Megawatt and James
Or even a pipe to carry the air instead of a wire for electricity?
Looks like the OP hasn't been back since.
Reactions: Megawatt
Probably because of the price of wire. 1300 feet for a neutral, 2 hots and an equipment ground. That’s 5200 feet of wire. Not cheap
Reactions: nicebutdim and DPG
A standard mile of cable!
Reactions: Megawatt and DPG
Yes, much better/cheaper to use an engine driven compressor, or even a generator and compressor. Especially considering how much cheaper fuel is over there than it is here.
That would be a very large pipe to compensate for the pressure loss, this works much tbe same way voltage drop does.
3 phase run of 1300 feet
Davis PB,
brianmoooore,