Eh up
We all know about the duff max Zs tables in the OSG (Table B6) and GN3 (Table A4)... in fact, I've only just recently updated my GN3, and I'm pleased to say they have reprinted it and it now has the correct tables in.
I've noticed in my (early-purchased, with dodgy table B6) OSG that it gives information entirely contradictory to BS7671.
And it's not about something obscure, it's about whether a cable buried <50mm deep in a wall, within the prescribed zones, needs an RCD or not. The regs says it does (522.6.202 (i) and the sentence below (ii)). The OSG says it doesn't (section 7.3.2, p77).
Also, the regs gives you an option that a cable shall "be provided with mechanical protection against damage sufficient to prevent penetration of the cable by nails, screws and the like" (522.6.204 (iv)) WITHOUT RCD protection (as with all the other methods of protection mentioned in 522.6.204), whereas the OSG says that cables protected in this way (mechanical protection that is not earthed) DOES need an RCD.
How has this f'kup occurred? Because in this edition of the OSG they re-ordered the "options." In the old green OSG the options were listed "i" to "vi", where "v" was about the zones. So the sentence, "... cables not installed as per i, ii, iii or iv but complying with v must be protected by a 30 mA RCD." In the new yellow OSG the options are listed (a) to (f), but in a different order, with the one about the zones now being (b), with (e) being about unearthed mechanical protection. But the sentence at the bottom reads, "... cables not installed as per a, b, c or d but complying with e must be protected by a 30 mA RCD."
So they changed the Roman numerals to letters, but failed to take into account that they'd re-ordered the list.
Muppets.
I don't think this is a trivial error, either. Many people "learn" the regs using the OSG (I know they shouldn't, but they do) and it's more tempting to look there than an £85 500 page book. So, there are probably people installing lighting/cooker/shower cables <50mm from the surface within the prescribed zones without RCD protection, who think they are complying with the regs.
I can't understand why this isn't in the errata.
Does anyone have a recently-printed version of the OSG? It will have the correct Table B6 (without a supplied errata sheet). Would you mind checking P77, to see if they've fixed this?
Muppets.