Currently doing an EICR on 2 neighbouring propertys... 1 had a new consumer unit done within the last 5 years and 1 has the original unit.
These property's are supplied overhead and the original unit has a TT system installed.
The Electrician that has installed the new unit has left the TT earth in but has installed 16mm earth off the neutral as if a TN-C-S system and I'm getting an adequate Ze reading (0.16).
Is there a way to check that this is actually a PME arrangement or should I contact the provider? Will they even know??
 
Hi - If the DNO has recently upgraded the network to permit use of TNCS at the property they will likely have added a PME label at the cutout. Hopefully you’ll also see new earth rods at nearby power poles outside. By all means check with the DNO to confirm.
 
You should ask the PME. You could test the Ze, but the test result might confuse the issue.

I‘ve worked on a couple of properties, that have overhead supplies, that have been converted to pme by the DNO.

Has the main earth been terminated into the supply head and been sealed?
 
Could have been converted to PME by DNO and the earth rod left connected. As above. Would be easy to double check with the DNO though.
 
You should ask the PME. You could test the Ze, but the test result might confuse the issue.

I‘ve worked on a couple of properties, that have overhead supplies, that have been converted to pme by the DNO.

Has the main earth been terminated into the supply head and been sealed?

You have the ability to communicate with an earthing system! I am impressed. ;)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Can I test for PME?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Advert

Thread statistics

Created
K-Electric,
Last reply from
K-Electric,
Replies
6
Views
3,960

Advert