Coding taken to far

Discuss Coding taken to far in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

scotsparky

-
Arms
Reaction score
12
I have been given a PIR and asked to do all codes 1 and 2 ok but the tester has applied interesting code2s heres a few the list is not endless.

1 Incorrect screws in panel cover.
2 dust at bottom of d.b
3 No 230V labels.
4 Panel has no markings sayiny 2 different wiring tyopes (labeled at origin)
5 light in switchroom not bright enough. (its a 5ft single and room is 10ft square)


anyone else think these codings are more like 4s notr 2s

By the way the same guy that did the test verified the results is this allowed on an NICEIC PIR i am not sure of the ruling.
 
imo lables diff colour should be something carried by tester
5ft fitting should be ok but should be em fitting
incorrect screws 4
dust ffs picky
 
Half of them shouldnt have been mentioned never mind being worthy of a code. On my PIR's I tend to list coded items first, then include the recommendations after to back up any letters that I also submit.

Didnt think 230V labels were required as that was the assumption on removing a cover, warning required for higher voltages only if unexpected :)
 
230v labels only required in equiptment where voltage would not be expected,a db is obvious so what is the tester on about,415v labels required deffo,plus next test labels,2 wiring colours only need be at origin,but i normally put them on all dbs because they dont cost much.
 
1 Incorrect screws in panel cover.
2 dust at bottom of d.b
3 No 230V labels.
4 Panel has no markings sayiny 2 different wiring tyopes (labeled at origin)
5 light in switchroom not bright enough. (its a 5ft single and room is 10ft square)

QUOTE]

I bet he has names for all his screwdrivers too.
 
Just seen more ant this is the best so far.
Code 1 fault Urgent attention and i quote.

"Over the next 10 years the trunking and conduit will corrode recommend installing seperate CPCs for all circuits. "


1 When did the old PME system get outlawed?
2 Thats 2 periodics away surely any degridation will be pickked up on the next periodic in 5 years.
 
Just seen more ant this is the best so far.
Code 1 fault Urgent attention and i quote.

"Over the next 10 years the trunking and conduit will corrode recommend installing seperate CPCs for all circuits. "

Did he, by any chance,mention if I was coming into a lot of money during that time :)
 
very keen, like has been said, most should be 4s if coded atall. Might just be a case of not having much work on so trying to beef up the potential for remedial works?? either way it's not good!
 

Reply to Coding taken to far in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock