Evening all
I went to quote a job a few days ago. On a TT system and an old Contactum board no RCD protection.
Client wants power to her garden building.
Now the OCPD and the leg supplying the building don't need RCD protection. A new DB will be installed in the GB and an earth rod.
Do I need to do anything with the House DB? I'm not working on any circuits that require RCD protection, on the face of it the earthing arrangements seem in order pending testing.
 
Last edited by a moderator:
Why doesn't the leg need rcd protection does the existing protective device provide adequate fault protection.
 
Im assuming being a TT system that the earth fault loop impedance will not be achieved to the shed. This being the case how are you going to achieve fault protection without RCD.
 
  • Like
Reactions: buzzlightyear
You saying that has just made it land in my brain, I was having a serious case of writers block.
As it's a TT system the OCPD won't provide FP as it won't meet the disconnection time thus the RCD requirement is needed for fault protection..... blimey lol
You use far too many acronyms.
 
  • Funny
Reactions: Dave OCD

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Email
Joined
Time zone
Last seen

Thread Information

Title
DB with no RCD, new circuit?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Voltus,
Last reply from
littlespark,
Replies
9
Views
2,591

Advert