Having spend my life in an industrial maintenance roll I seem to have forgotten all I learned, could somebody help me on this one.
Its a new build and I am looking at the demand, where am I going wrong.
Diversity for total demand
Curcuit MCB
Upstairs Ring 32A
Downstairs Ring 32A
Lighting Upstairs 1 (5 Lights) 6A
Lighting Upstairs 2 (7 Lights) 6A
Shower 8KW 35A
Cooker Oven 7.2kw 32A
Smoke Alarms x 2 6A
So apply diversity?
Ring
100% of largest then 40% of other = 44.8A
Lighting 66% of demand (100w) = 66% 0f 5.22a = 3.45A
Shower 100% = 35A
Cooker 10A + 30% of fl in excess = 16.39A
Smokes No diversity ?? = 6A
Total demand = 105.64A
and I haven't got the spec for the boiler yet 