Am I correct in saying I can install a single pole Type A 30ma RCBO to feed an Hypervolt EV charger? the supply cable is SWA and the Hypervolt has in built 6ma DC RCD protection. The consumer unit is a Lewden board so would ideally like to install a SP RCBO type A, any issues with this? its a TNCS system.

Thanks in advance..
 
As above, the RCD is required to break all live conductors (including the neutral).
 
Hi,
Am I correct in saying I can install a single pole Type A 30ma RCBO to feed an Hypervolt EV charger? the supply cable is SWA and the Hypervolt has in built 6ma DC RCD protection. The consumer unit is a Lewden board so would ideally like to install a SP RCBO type A, any issues with this? its a TNCS system.

Thanks in advance..
Lewden / control gear DP Type A RCBOS are around £20 any branch of Rexel or Denmans have them.

No excuse not to fit one as they are so readily available.

If using SWA you should really run a cat5e for he grid ct or use ev ultra cable as the charger needs the ct clamp to enable a whole host of features, the charger comes with the grid ct for a reason.

If you do not fit it then make sure you set the ALM correctly or it will not charge when you want it to.

Without sounding Harsh, if you are asking this question it suggests you havent read the instructions/tech support on the hypervolt website!
 
As above. You need to run a data cable when installing a hypervolt, as they insist on a CT clamp being fitted (It is supplied). The warranty will not he valid if you don't install the CT. I like the hypervolt and the customer service is good (Thanks @Gavin for recommending them), but I will be selective in using them because of the necessity of using the CT.
 
As above. You need to run a data cable when installing a hypervolt, as they insist on a CT clamp being fitted (It is supplied). The warranty will not he valid if you don't install the CT. I like the hypervolt and the customer service is good (Thanks @Gavin for recommending them), but I will be selective in using them because of the necessity of using the CT.
can anyone buy the Hypervolt chargers or do you have to become one of their approved installers?
 
can anyone buy the Hypervolt chargers or do you have to become one of their approved installers?
I believe anyone can buy them, but if you are a hypervolt installer you get them approx £50 cheaper.
 
  • Like
Reactions: diditrain
I think you only get a years warranty instead of three if you don't register.
 
  • Like
Reactions: diditrain

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Norfolk
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Do I need to install an RCD for a Hypervolt EV charger
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
8

Advert

Thread statistics

Created
paulsaunders16,
Last reply from
Aaron b,
Replies
8
Views
5,737

Advert