james king

hi all! we were at a job to day and the water was not earthed but the home owner said the spark did not have to earth it because it was plastic incomer! but then from the stop tap was copper! is this correct? i was to busy chasing walls to here what my boss said
 
hope your boss told him he was totally wrong. metallic water pipe needs bonding whether the incomer is plastic, lead or even kryptonite.
 
Last edited:
Regulation 544.1.2 buddy.
 
hope your boss told him he was totally wrong. Metallic water pipe needs bonding whether the incomer is plastic, lead or even kryptonite.

:d:d:d and :D:D:D





My smilies have started learning the alphabet,where are they gone:)
 
Last edited:
My bonding knowledge is alot to be desired.
Do I remember a post last week of someone stating that bonding services with incoming plastic is liable to introduce an earth potential?
 
Sort of Simon. The actual plastic incomer more than likely will not introduce a potential, so you will not need to bond that. Where is can go wrong is if then the house installation is copper there is a good chance that because we are also bonding the gas pipe which normally is metal, and that and your copper internal water pipe will somewhere in the house meet up normally at a boiler.

So when you bond the internal water installation what your effectively doing is supplementary bonding. To make sure that all the pipework is at the same potential.
 
Sort of Simon. The actual plastic incomer more than likely will not introduce a potential, so you will not need to bond that. Where is can go wrong is if then the house installation is copper there is a good chance that because we are also bonding the gas pipe which normally is metal, and that and your copper internal water pipe will somewhere in the house meet up normally at a boiler.

So when you bond the internal water installation what your effectively doing is supplementary bonding. To make sure that all the pipework is at the same potential.

Gotcha so if both services were plastic incoming there would be no need to main bond? As you wouldn't need to make the services the same potential. ?
 
That is right. niether the gas or water installations would be able to introduce a potential to earth if they were both supplied in plastic. It would be equivelent to bonding a metal window or door frame or any other metallic object in the installation that would not have the ability to produce a potential.
 
but, as the water pipes are fixed to walls and pass through walls, can they not introduce earth potential through the fabric of the building?
 
Here's some guidance from the IEE, not updated to 2008 but still has some relevant points and some interesting stuff on the 'water is a good conductor' myth:
 

Attachments

Suppose it could if it's in close vicinity to any structural steel?

If you were using the structual steel as an earth electrode as in reg 542.2.1 theorectically you could get a problem. As the reg says you can use either the foundation metalwork or welded ree bar, note welded and not tied, but these systems would not be readily accessible as they would be embeded. So the scenario could be if you drilled into your wall and hit a ree bar screwed a metal pipe clamp to the wall with your metal screw and then fitted your pipe, if there was an earth fault you could make that pipe live, it's possible but un-likely. Besides as your making this system a TT it would be RCD protected.

As for a normal metal frame building as the new factories are, you actually bond the structual steelworks. ie the U and I beams back to your MET. So again if your services for gas and water were plastic but then metal and attched to any of the beams you still would not need to bond those pipes, same way as metal racking in such a building does not need bonding, even if it's bolted to the metal of the building.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
earthing water pipes
Prefix
N/A
Forum
Electrician Forum
Start date
Last reply date
Replies
13

Thread Tags

Advert

Thread statistics

Created
james king,
Last reply from
malcolmsanford,
Replies
13
Views
10,196

Advert