For you guys that do EICRs. When carrying out a periodic condition reports on an older installation that are used by the general public. Re special areas containing showers, bathrooms, basins, in other words wet areas, if no RCD protection would you code it C3 as a recommendation to install RCD or not at all as done to regs at time of install? As open to the public this would classed as commercial not domestic. I would say code 3 myself, but would like your opinions please.
:thinking2:
 
For showers and bathrooms not basins it would depend on whether supplementary bonding were correctly in place. (and main bonding).
If the bonding was sufficient for the area then I would agree with a C3.
For public areas I would expect the risk of accidents would be fairly high so I would want to see RCD protection in place, but would only recommend.
If there were no bonding in place then C2 as it would be (apparently) very dangerous, though would presumably have worked safely for years.
But it would be safe, if there were no faults!
 
  • Like
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
England
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Retired Electrician

Thread Information

Title
EICR older installations
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
1

Advert

Thread statistics

Created
driverman,
Last reply from
Richard Burns,
Replies
1
Views
997

Advert