Even if the supply cabjes are meters tails to the double poll switch?

You've got two different things going on here which makes this situation complicated.
1 - the standard problem of metal CU and TT. Most agree best practise is a front-end RCD. The 17th edition required it in most circumstances, and the 18th just has a higher spec for the supply (belt and braced secured and double insulated etc. ) but doesn't require it.

2 - the fact that you are almost certainly dealing with a special location, whether it be a caravan supply or a mobile home supply. Whichever it is there are regs in both sections requiring an RCD in the final circuit supplying it.

Put it all together - the best place for an RCD for both 1 and 2 is where loz2754 said which is also where section 7 says there should be one (protecting a final circuit supplying the mobile home or park home / protecting the supply to the caravan)

The only fly in the ointment is that section 7 says the supply RCD should be 30ma which would leave no discrimination. As there are downstream RCDs for everything and it's a distribution circuit I'd be inclined to stick with the 300ma suggestion unless anyone has a better idea.
 
Fault protection should operate before 50 volticles
Agree. The ZS is pretty good for a TT as there is an all year round high water table. So do i ho for s timed 100mA, timed 300mA or just a 300 mA?

if i went for a standard 300mA snd <50v it would still give us over a 100ohms comfort zone even if it doubled to 60ohms.
Thanks all.
 
Agree. The ZS is pretty good for a TT as there is an all year round high water table. So do i ho for s timed 100mA, timed 300mA or just a 300 mA?

if i went for a standard 300mA snd <50v it would still give us over a 100ohms comfort zone even if it doubled to 60ohms.
Thanks all.
One last point...

i found this really good article last night that summarises the key points.

 
That's a very good article. Thanks.
I'd found a very similar article (I thought it was same one at first) and the same conclusions are reached but it includes a bit of history too:

I personally think an exclusion allowing plastic containment for RCD enclosures would help matters a great deal. I notice that DNO's seem to be allowed to to fit plastic contained isolators....
(I wonder how many fires have ever started in an RCD enclosure versus electric shock deaths on TT earthed installations)
 

Reply to Existing split load 17th Install RCD question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K
See this time after time - poor installation: new split load board on a re-wire tt installation. The main switch is not a time delay rcd. The...
Replies
2
Views
357
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
902
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
763

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock