Even if the supply cabjes are meters tails to the double poll switch?
You've got two different things going on here which makes this situation complicated.
1 - the standard problem of metal CU and TT. Most agree best practise is a front-end RCD. The 17th edition required it in most circumstances, and the 18th just has a higher spec for the supply (belt and braced secured and double insulated etc. ) but doesn't require it.
2 - the fact that you are almost certainly dealing with a special location, whether it be a caravan supply or a mobile home supply. Whichever it is there are regs in both sections requiring an RCD in the final circuit supplying it.
Put it all together - the best place for an RCD for both 1 and 2 is where loz2754 said which is also where section 7 says there should be one (protecting a final circuit supplying the mobile home or park home / protecting the supply to the caravan)
The only fly in the ointment is that section 7 says the supply RCD should be 30ma which would leave no discrimination. As there are downstream RCDs for everything and it's a distribution circuit I'd be inclined to stick with the 300ma suggestion unless anyone has a better idea.