I want to connect an external socket to a fused spur which is inside the house. I have 1.5mm 3 core cable but it is 16 amp. Can this be used ?
Its going through a nine inch wall, no further. Is 16 amp cable ok ?There are other things to consider, but for a short distance, 1.5mm2 3 core is ideal .