Looking to get electrics in my shed best solution I can think of is.... 6mm from the main board in my house out to a waterproof junction box, connected up to swa which then goes off to the shed and connects to a sub board. That then controls the power there on wards.. any suggestion on better ways ? Or is that good enough. Thanks
 
Looking to get electrics in my shed best solution I can think of is.... 6mm from the main board in my house out to a waterproof junction box, connected up to swa which then goes off to the shed and connects to a sub board. That then controls the power there on wards.. any suggestion on better ways ? Or is that good enough. Thanks
file:///C:/Users/Pete/Desktop/Petes%20resources/Garage-Shed%20Supplies(1).pdf
 
  • Like
Reactions: buzzlightyear
and don't forget to pay their wage for experience and knowledge.
 
  • Optimistic
Reactions: Pete999
Looking to get electrics in my shed best solution I can think of is.... 6mm from the main board in my house out to a waterproof junction box, connected up to swa which then goes off to the shed and connects to a sub board. That then controls the power there on wards.. any suggestion on better ways ? Or is that good enough. Thanks

Might be OK, might not.

For a start, how about:
Supply/earthing system?
Anticipated load?
Length of circuit?
Installation method (indoors and out)?
Circuit protection?
No. & type of circuits in shed?
Extraneous conductive parts in shed?
 

Attachments

upload_2017-11-24_15-20-14.png
 
Why t&e to junction box on wall and then swa why not continuous swa
 
  • Like
Reactions: DPG
Remember if the T&E is not surface run then it will need an up-front RCD.
 
  • Agree
Reactions: Des 56
Why t&e to junction box on wall and then swa why not continuous swa
Probably because it's far easier to run a Twin and earth integrally, jointing in a Wiska box and the continuing the run in SWA, not ideal, but far more practicable. IMO
 
  • Like
Reactions: DPG
If I was going to do it it that way I'd make sure I protected the cable going out to the Shed with a timed delayed RCD, then the DB in the Shed can have a standard 30mA main switch. Depending on your incoming supply your also probably need put in an earth stake anyway (something I tend to do for any TN systems anyway).

You don't seem to have much confidence in your sparks.
 
If I was going to do it it that way I'd make sure I protected the cable going out to the Shed with a timed delayed RCD, then the DB in the Shed can have a standard 30mA main switch. Depending on your incoming supply your also probably need put in an earth stake anyway (something I tend to do for any TN systems anyway).

You don't seem to have much confidence in your sparks.

Why?
 
  • Like
Reactions: DPG

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Feed to my shed need suggestions
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
joshapps,
Last reply from
123,
Replies
24
Views
2,087

Advert