In reply to questions;
- it was tested with appliances still plugged in
- I wasn't given any test results
- Don't know if a ramp test was done or not
In terms of reconfiguring the consumer unit, any indication how successful that is likely to be and roughly how much it would cost?
If testing was only done with everything plugged in, it could just as well be an intermittent wiring fault, there is no way of knowing. Hopefully you didn't pay too much for what appears to be quite limited testing and no results.
My preference would be to locate the fault(s) - in either the wiring and/or appliances - and fix - but sometimes when intermittent, a fault can prove quite elusive. If you have a freezer full of food you don't want trashed, it might be more pragmatic to have that circuit on it's own RCBO - separate from the other 5 circuits - though if the fault is actually on this circuit it won't help, the RCBO will trip instead of the RCCB. An RCBO costs around £30 or so, depending on the brand, plus 1 hours labour might be enough to reconfigure this.