Just wondering if others make off their armoured glands at both ends has have worked with sparks previously and seem to have different takes on it. My thoughts are that if glanded and so earthed at origin is acceptable so if for example supplying a sub board in garage a plastic gland at the board is fine and SWA glanded at origin of supply so house board is fine?
 
A gland at both ends provides additional cable restraint that a stuffing gland won't to the same level. Should always gland the supply side as a minimum in my opinion. Personally I would always gland both ends, even into a plastic db. Obviously if the armour is also used as CPC then there must be continuity somehow.
 
I'd call that disgraceful, sub standard work. 134.1.1 for starters.
 
Last edited:
Yea should gland both ends,only exemption is if it’s a TT system,to separate the Earthing.
 
Why do you think swa glands come in packs of 2?

the right tools for the right job.
 
As above, plastic glands for TT isolation purposes.

Maybe other odd cases, such as small 3-core SWA in to an outdoor light where they did not really expect a metal gland or provide adequate space for one.
 
Regulation wise my memory tells me that the SWA should be glanded / earthed at at least one end and preferably the supply end.

I think this is why some people think that glanding at only one end is acceptable.
 
  • Like
Reactions: pc1966
Regulation wise my memory tells me that the SWA should be glanded / earthed at at least one end and preferably the supply end.

I think this is why some people think that glanding at only one end is acceptable.
That's my point Ferg. I possibly understand the use of SWA gland for adding support to cable or using the SWA for earthing but in terms of an actual shock risk if cable aupported i fail to see one. A live conductor needs to come in contact with the steel sheathing and if this is earthed at supply end all good.
 
Why do you think swa glands come in packs of 2?

the right tools for the right job.
You've not actually explained the logical reason why though if cable supported and not using SWA for earthing?
 
Even if you have a CPC core it is still better to gland both ends so the armour is providing a CPC path. Not just in cases where the armour may not meet adiabatic limits, but just as it reduces the risk of an open CPC if you have parallel paths.
 
Even if you have a CPC core it is still better to gland both ends so the armour is providing a CPC path. Not just in cases where the armour may not meet adiabatic limits, but just as it reduces the risk of an open CPC if you have parallel paths.
Now that explanation and reasoning I can go with ?
 
  • Like
Reactions: pc1966
While it is not a common electrical requirement as such, if you correctly terminate the outer screen to the metal work where a cable enters by a gland or connector providing 360 deg contact as you get much better screening of high frequency noise from a EMC perspective.

In power systems this is only likely to be lightning surges, but it is a far more critical requirement for coax cable where taking the braid/shield in as a "pig tail" is very bad news from a radio screening and constant-impedance perspective.
 
Why do you think swa glands come in packs of 2?

the right tools for the right job.
I think I've heard of them....do they come with an instruction pack?

IMG_0193.JPG

IMG_0189.JPG

IMG_0190.JPG
 
  • Funny
Reactions: pc1966

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
gland swa at both ends?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
13

Advert

Thread statistics

Created
JohnS888,
Last reply from
ipf,
Replies
13
Views
7,314

Advert