Morning Men, Women & Mike...

Just a quick one, and i realise im going to sound completley stupid here ...

I've been called to a static caravan 3 times in the last week - the last time being monday morning. There had been no power to the caravan, although no breakers tripped out either in the distribution board outside or the consumer unit inside. I asked neighbours and the park owners whether they had been having power cuts recently and nope - it's just this one caravan. This too me suggests a loose connection somewhere, the first time i went i did a thorough test of the install with all readings more than acceptable - i also checked for loose connections on the incomer - literally couldn't find a thing. Second time i went, i literally repeated myself and again nothing - it doesn't help with the fact everytime i got to the static the power had come back on...

Anyway the third time on monday, i just replaced the RCD - even though the old RCD tripped out in accordance with regs at 1/2 1 and 5 on both cycles and the test button worked ... no idea why i replaced the RCD, but i was kind of struggling. Anyway since then there hasn't been a problem...

So my newbie question is : Can RCD'S actually go faulty even though they test and trip out at the required times?

(I've come across RCD's and MCB's that don't pass the juice across before, but everytime i was there this one was working exactly as it should be.)
 
It's very unlikely to be the RCD unless it was actually physically tripping, it would be better odds on an intermittent leakage problem and someone resetting it without the knowledge of the person you spoke to. That said anythings possible so maybe soak test the RCD on a known-good installation for a week or so or I guess with the low price of them nowadays it's probably not worth it so just dump it as suspect if the problem in the caravan doesn't reoccur.
 
  • Like
Reactions: 1 person
I would think that perhaps there was a strand of conductive dust or cable that was causing the fault (perhaps even an intermittent loose connection generating enough spiking to cause the RCD to trip) that has been removed by your actions.
It could also be that the RCD was tripping at 16mA and there is an intermittent fault to say 20mA and your new RCD is tripping at 27mA or figures to that effect.

The most likely cause is the user realised the power tripped out every time they used the kettle and have now replaced the kettle without telling you.:smile5:
 
  • Like
Reactions: 2 people
It's very unlikely to be the RCD unless it was actually physically tripping, it would be better odds on an intermittent leakage problem and someone resetting it without the knowledge of the person you spoke to. That said anythings possible so maybe soak test the RCD on a known-good installation for a week or so or I guess with the low price of them nowadays it's probably not worth it so just dump it as suspect if the problem in the caravan doesn't reoccur.

I couldn't help myself lol, I would have to find out.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Morning.
Prefix
N/A
Forum
Electrician Talk
Start date
Last reply date
Replies
5

Thread Tags

Tags Tags
morning

Advert

Thread statistics

Created
markc123,
Last reply from
Marvo,
Replies
5
Views
55

Advert