pjb1
Hello everybody
Went to do my first Periodic Inspection Report on a single storey flat for a letting agent,not yet occupied. TN-CS suppiled 25mm tails 16mm Earthing conductor Good Start? enter the property.
Found good old rewirable fuse consumer unit. in the bottom of the enclosure a 2" hole not good possible to touch a live busbar. straight away Code 1 me thinks?
Isolated and removed fascia what a rats nest of wiring all single, Bonding cable 2.5mm earth cable code 4
1/ Cooker 6mm/2.5mm single type of wiring B pvc in Metal Conduit, Continuity and I/R tested fine.
2/Ring final circuit for socket end to end continuity on neutral and cpc live conductor meter reading show open circuit.
Spent the rest of my time there trying to find out why live conductor was not in a ring went from socket to socket looking for broken or loose conductor checked to see if termination tightened onto cable insulation.
Any way you guys can help to solve this problem ? Or do I have to break the ring down completely and test continuity ie consumer unit to first socket, first socket to second socket etc etc. But still leaves me guessing where the ring has been split when I come to the last socket.
I have let the letting agent know, And advise them that the Installation is not safe, Would it be better just to change the socket RFC to a radial circuit and down rated the protective devise? Also advised them to have the consumer unit changed.
As it a single store would I still need to use a split load dual rcd consumer unit, Or would I be able to replace it with a board that all circuit are rcd protected?
Went to do my first Periodic Inspection Report on a single storey flat for a letting agent,not yet occupied. TN-CS suppiled 25mm tails 16mm Earthing conductor Good Start? enter the property.
Found good old rewirable fuse consumer unit. in the bottom of the enclosure a 2" hole not good possible to touch a live busbar. straight away Code 1 me thinks?
Isolated and removed fascia what a rats nest of wiring all single, Bonding cable 2.5mm earth cable code 4
1/ Cooker 6mm/2.5mm single type of wiring B pvc in Metal Conduit, Continuity and I/R tested fine.
2/Ring final circuit for socket end to end continuity on neutral and cpc live conductor meter reading show open circuit.
Spent the rest of my time there trying to find out why live conductor was not in a ring went from socket to socket looking for broken or loose conductor checked to see if termination tightened onto cable insulation.
Any way you guys can help to solve this problem ? Or do I have to break the ring down completely and test continuity ie consumer unit to first socket, first socket to second socket etc etc. But still leaves me guessing where the ring has been split when I come to the last socket.
I have let the letting agent know, And advise them that the Installation is not safe, Would it be better just to change the socket RFC to a radial circuit and down rated the protective devise? Also advised them to have the consumer unit changed.
As it a single store would I still need to use a split load dual rcd consumer unit, Or would I be able to replace it with a board that all circuit are rcd protected?