Good evening everyone,

So I have a "customer" wanting power supplied to an outside shed they are building in the near future which is going to serve as a sort of outside bar type area.

All wiring will be within the shed and the circuits installed will be a radial power circuit and a lighting circuit. I plan to wire these in singles within plastic conduit and have it surface mounted. Nothing special here.

I plan to use 2 core SWA to supply this, either in 2.5mm² or 4mm² (most likely 4 to future proof it.) which will be buried through the garden, most likely installed within cable ducting.

The supply earthing arrangement is PME, so I'm thinking this shed will need to have its own earth rod installed and the earth from the house terminated and isolated from the consumer unit within the shed.

There is a little snag however, and that is the placement of the consumer unit within the property. It is located inside the downstairs toilet, in the top corner. There is no easy way to route cables to this location as the utility room on the other side of the wall has a fully tiled floor. (I have attached a picture of the back door and utility room and the wall which is on the other side from the consumer unit.)

My plan to tackle that would be to run a length of conduit from one wall, onto the ceiling and then back down onto the wall which backs outside (this is a utility room and the "customer" is fine with this arrangement), have this connected to an external weatherproof box and then via appropriate connectors, glands and the likes link onto the SWA which will be clipped direct to the wall and then run down the side of the house and then off to the shed.

This is my first actual domestic setting job, and I'm just wanting a bit input and thoughts from the experience of people on the forums. Would you suggest anything? Do anything differently? I'm interested to hear!

20170620_193604.jpg 20170620_193616.jpg 20170620_193630.jpg


Thanks for reading!

20170620_194739.jpg
 
Good evening everyone,

So I have a "customer" wanting power supplied to an outside shed they are building in the near future which is going to serve as a sort of outside bar type area.

All wiring will be within the shed and the circuits installed will be a radial power circuit and a lighting circuit. I plan to wire these in singles within plastic conduit and have it surface mounted. Nothing special here.

I plan to use 2 core SWA to supply this, either in 2.5mm² or 4mm² (most likely 4 to future proof it.) which will be buried through the garden, most likely installed within cable ducting.

The supply earthing arrangement is PME, so I'm thinking this shed will need to have its own earth rod installed and the earth from the house terminated and isolated from the consumer unit within the shed.

There is a little snag however, and that is the placement of the consumer unit within the property. It is located inside the downstairs toilet, in the top corner. There is no easy way to route cables to this location as the utility room on the other side of the wall has a fully tiled floor. (I have attached a picture of the back door and utility room and the wall which is on the other side from the consumer unit.)

My plan to tackle that would be to run a length of conduit from one wall, onto the ceiling and then back down onto the wall which backs outside (this is a utility room and the "customer" is fine with this arrangement), have this connected to an external weatherproof box and then via appropriate connectors, glands and the likes link onto the SWA which will be clipped direct to the wall and then run down the side of the house and then off to the shed.

This is my first actual domestic setting job, and I'm just wanting a bit input and thoughts from the experience of people on the forums. Would you suggest anything? Do anything differently? I'm interested to hear!

View attachment 36943 View attachment 36944 View attachment 36945


Thanks for reading!

View attachment 36946
what about running it under the plinth of the cupboards cutting a hole and fishing it up the wall to the consumer unit? Being a new build I would of thought they are stud walls? There might be a nogging at around 1200mm so you could cut a 1 gang box in with a multi tool and use a blank plate in the downstairs toilet or put the piece back in you've cut and fill the whole and the customer can tosh the wall which isn't going to be very big in a downstairs WC. Failing that pull the carpet back up stairs and use a solid board cutter and inserts to get a route to outside then conduit down the wall. Conduit across the ceiling will look gash imo and you might have to use metal supports which will make it look even worse. Another solution but not ideal would be to put a switch fuse in the meter cupboard and split the tails with Henly blocks and run the SWA from there.
 
Good evening everyone,

So I have a "customer" wanting power supplied to an outside shed they are building in the near future which is going to serve as a sort of outside bar type area.

All wiring will be within the shed and the circuits installed will be a radial power circuit and a lighting circuit. I plan to wire these in singles within plastic conduit and have it surface mounted. Nothing special here.

I plan to use 2 core SWA to supply this, either in 2.5mm² or 4mm² (most likely 4 to future proof it.) which will be buried through the garden, most likely installed within cable ducting.

The supply earthing arrangement is PME, so I'm thinking this shed will need to have its own earth rod installed and the earth from the house terminated and isolated from the consumer unit within the shed.

There is a little snag however, and that is the placement of the consumer unit within the property. It is located inside the downstairs toilet, in the top corner. There is no easy way to route cables to this location as the utility room on the other side of the wall has a fully tiled floor. (I have attached a picture of the back door and utility room and the wall which is on the other side from the consumer unit.)

My plan to tackle that would be to run a length of conduit from one wall, onto the ceiling and then back down onto the wall which backs outside (this is a utility room and the "customer" is fine with this arrangement), have this connected to an external weatherproof box and then via appropriate connectors, glands and the likes link onto the SWA which will be clipped direct to the wall and then run down the side of the house and then off to the shed.

This is my first actual domestic setting job, and I'm just wanting a bit input and thoughts from the experience of people on the forums. Would you suggest anything? Do anything differently? I'm interested to hear!

View attachment 36943 View attachment 36944 View attachment 36945


Thanks for reading!

View attachment 36946
Crikey did you install that SWA?
 

Reply to Power to shed. Thoughts? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I'm a DIY'er looking to build a 6x8 shed in my backyard in Colorado. I'm installing a gravel pad first, with 4 concrete Sonotube...
Replies
1
Views
353
Can a domestic consumer unit feed another consumer unit, via the Main Switch. Details are: domestic property with 100A single phase supply...
Replies
9
Views
477
Hi, I have a client with a small caravan site, approx 5 hookups. His old toilet block was nothing much more than an old shed. He's now 'upgraded'...
Replies
2
Views
581
Hi All I'm new here. I have just finished my NVQ and waiting to do my AM2. I have a question on selectivity as it has always slightly confused me...
Replies
5
Views
815
I've wired some cable to a small 3x3 shed with 2 gpos, a 15a GPO, and a light. The shed is about 2m away from the house on a concrete slab. The...
Replies
0
Views
566

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top