Hi everyone I've come across a weird situation where somebody has got new sockets added, but from the board it is a radial in 6mm as there is one set of cables into the breaker, then when you look at the sockets (2 double sockets) it's got 2, 2.5mm cables going into both like it's a ring
Does this seem acceptable

I have drawn what I think has happend and if anyone thinks it's acceptable

14489881011481906294751.jpg14489881011481906294751.jpg
 
Commonly known as a lollipop circuit, its not a standard bs7671 paint by numbers circuut so you have to actually think about it a little when it comes to testing it
 
It's a lollypop circuit. Perfectly acceptable providing that all the usual requirements are met regarding overcurrent protection, RCD protection, Zs, ring continuity, etc, etc.


Edit: Snap!
 
  • Like
Reactions: 1 person
Ok thanks guys it's not acceptable with a 40 amp breaker tho isit because the ring should be be 32 amp max breaker shouldn't it
 
Lollipop circuit, don't like em, don't use em
 
Ok thanks guys it's not acceptable with a 40 amp breaker tho isit because the ring should be be 32 amp max breaker shouldn't it
it should be on a 32A MCB. soon chamge it. otherwise, as before. if readings are OK.....
 
Ok thanks guys it's not acceptable with a 40 amp breaker tho isit because the ring should be be 32 amp max breaker shouldn't it
But your drawing states 32 amperes.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
radial and ring
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
9

Thread Tags

Advert

Thread statistics

Created
Dan Brown,
Last reply from
Dan Brown,
Replies
9
Views
1,358

Advert