Hi there I have a problem with rcd tripping in a department store, I changed 2 old board which where re wire fuses to dual rcd boards which all the other circuits stand but 2 circuit breakers which one does a few track lights for display and the other does 2 led tornado fittings when I energies the tornado fittings it trips one side of the split rcd and when I energies the track lights it takes out two of the rcd at the same time, it’s a decent sized store and iam struggling to faukt find on it any help would be greatly appreciated
 
I take it you have checked for the usual suspects like insulation resistance & borrowed neutrals? If the RCDs are tripping! If it's mcbs how many fittings and what rating and type are the mcbs? Could be in-rush current if there are a lot of fittings!
 
Dual rcd boards could be affected by cumulative earth leakage across a number of circuits.

I would look for borrowed neutrals.... might be the case of doubling up a couple of circuits onto one.
Old stores would just have circuits added and modified as and when needed, quickly during closed, and no real design or testing done at the time.
 
Dual rcd boards could be affected by cumulative earth leakage across a number of circuits.

I would look for borrowed neutrals.... might be the case of doubling up a couple of circuits onto one.
Old stores would just have circuits added and modified as and when needed, quickly during closed, and no real design or testing done at the time.
Yeah my thought was maybe earth leakage but my mind was wondering to other things could it be possible to clamp the main earth in the board and see what iam getting down the earth or am I on the wrong path? Thanks a lot for the advice
 
I would say not as it may tell you some of the earth leakage but some will be lost to parallel paths. Usually you would clamp the live and neutral together for the circuit in question and look for the discrepancy. Tbh I have only used the conventional tried and tested methods for finding faults like this but they work without fail!
 
I take it you have checked for the usual suspects like insulation resistance & borrowed neutrals? If the RCDs are tripping! If it's mcbs how many fittings and what rating and type are the mcbs? Could be in-rush current if there are a lot of fittings!i
Dual rcd boards could be affected by cumulative earth leakage across a number of circuits.

I would look for borrowed neutrals.... might be the case of doubling up a couple of circuits onto one.
Old stores would just have circuits added and modified as and when needed, quickly during closed, and no real design or testing done
I would say not as it may tell you some of the earth leakage but some will be lost to parallel paths. Usually you would clamp the live and neutral together for the circuit in question and look for the discrepancy. Tbh I have only used the conventional tried and tested methods for finding faults like this but they work without fail!
Thanks a lot mate I have got alot to learn iam just trying to get there but by bit if I find will be sure to let you know
 
Had something similar a while ago where we were putting in a couple of RCBO boards to replace the 3036 boards, it quickly became apparent the multi gang switches and neutrals were not properly paired up, the installation had a 6 gang and 13 gang switch (18 gang grid 13 used), the 6 gang had 2 banks of 3 switches on 2 lives and 2 neutrals this ended up as a bank of 2 and 4 to get the lives and neutrals paired, the 13 gang
had groups of 2, 3 or 4 switches on one live and 2 or 3 neutrals it took a little while to unravel and get the switches grouped across the 4 lives and 4 neutrals but got there in the end.
What was interesting was the 5 yearly EICR's for the last 20 years had not found it but that's another story
 

Reply to RCD tripping on lighting circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been a while since I have been on here. I have been on an apprenticeship the last 3 years training in the BMS world. Taking that into...
Replies
7
Views
321
My friend just moved into a new build flat and its for a disabled person with a hydraulic lift to go to the upper floor. There was/is a leak...
Replies
8
Views
439
Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
791

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock