Circuit-breakers to BS-EN-60898 &RCBOs to BS-EN-61009-1 in non-preferred-current-ratings
Circuit-breakersto BS-EN-60898
RCBOsto BS-EN-61009-1 are sometimes encountered that have a rated-current other than thepreferred-values [ 3A , 6A , 10A ] listed in Table - 41.3. of BS-7671:2008:2011:
Themaximum-value of ( Zs ) for such a device , at a nominal-voltageof [ Uo - 230V ] can be found from the right-hand-columnof Table - 41.3. of BS-7671:2011:
Table- 41.3 , right gives therelevant-information .
Type - B circuit-breaker . having arated-current ( In ) of 8A ( or the overcurrent-characteristic of an8A Type - B RCBO ) the maximum-value of ( Zs )
at 230Vis 46 / In , = 46 / 8 = 5.75Ω .
Maximum( Zs ) for circuit-breakers to BS-EN-60898 and the overcurrent-characteristic of RCBOs to BS-EN-61009-1for instantaneous-operation giving compliance with the , 0.4 & 5 seconds ,disconnection-times at nominal-voltage [Uo - 230V ]
Table- 41.3.
Type- B - ( Zs ) Ohms for devices ofrated-current ( In ) 46/In .
Type- C - ( Zs ) Ohms for devices ofrated-current ( In ) 23/In.
Type- D - ( Zs ) Ohms for devices ofrated-current ( In ) 11.5/In.
Obsolete-Circuit-Breakers :
Maximum-valuesof ( Zs ) for circuit-breakers for which thisinformation is no longer given in BS-7671: can be obtained either from the edition of BS-7671: that was current when the deviceswere readily-available , or by reference to the manufacture’s - data .
Alternatively, for MCBs to BS-3871: Table - 2 , can be used to find the maximum-value of ( Zs ) at a nominal-voltage of [ Uo - 230V ]
For a Type- 2 circuit-breaker to BS-3871: having a rated-current ( In ) of 30A , the maximum-value of (Zs ) at 230V is [ 32.8 / In = 32.86/ 30 = 1.1Ω ]
Maximum( Zs ) for circuit-breakers toBS-3871: for instantaneous-operationgiving compliance with the , 0.4 & 5 seconds , disconnection-times at anominal-voltage of [ Uo - 230V ]
Type( Zs )
Type- 1 . Ohms - for device of rated-current- ( In ) 57.5/In
Type- 2 . Ohms - for device of rated-current- ( In ) 32.86/In
Type- 3 . Ohms - for device of rated-current- ( In ) 23/In
Type- 4 . Ohms - for device of rated-current- ( In ) 4.6/In
Type- B - ( Zs ) Ohms for devices of rated-current ( In ) 46/In .
Type- C - ( Zs ) Ohms for devices of rated-current ( In ) 23/In .
Type- D - ( Zs ) Ohms for devices of rated-current ( In ) 11.5/In .
Obsolete-fuses :
Maximum-valuesof ( Zs ) for fuses for which this information is no longer given in BS-7671: can be obtained either from the editionof BS-7671: that was current when the deviceswere readily-available , or by reference to the manufacture’s - data .
After 31 - December 2011 : one of these approaches is necessary forfuses to BS-88-2.2. : BS-88-6 : and BS-3871 : as data for them is notincluded in , BS-7671:2008:incorporating Amendment - 1 . 2011:
Overcurrent-protective-devices generally :
Forany type and rated-current of a fuse or overcurrent-circuit-breaker , includingall those mentioned above , the maximum-value of ( Zs ) can be found using the , formula given in Appendix - 3 of BS-7671: Where :- Zs = Uo /Ia .
Uo- is the nominal A.C. r/ms line-voltage to Earth - 230V.
Ia - is the current causing-operation of the protective-devicewithin the specified-time . such as 0.4 or 5 seconds . obtained fromthe manufactures - time / current-characteristics for the particular device-type and rating .
Supposed the manufactures - time / current-characteristic for a 400A - fuse , to BS-88-2.1. gives a value of ( Ia of 2840A ) for a disconnection-time of 5 - seconds . Using the above - formula , the maximum-value of ( Zs ) for the fuse , fordisconnection-time of 5 - seconds and anominal-voltage
( Uo ) of 230V , 230V ÷ 2840A = 0.08Ω
Measured- values of ( Zs ) taking account of conductor -temperature
It should not be forgotten that when comparing ameasured-valued of ( Zs ) with the maximum-value of ( Zs ) allowable for the device used for , fault-protection , account must betaken of the temperature and résistanceof the circuit-conductors . Appendix - 14 of BS-7671: refer .
Provethat the following table-provides instantaneous-disconnection for a BS-EN-60898 & BS-EN-61009-1 - Type B .32A Circuit--breaker using table 41.3. App - 3 .
Zs ≤ Uo /Ia . Table- 41B2
16[SUP]th[/SUP] Edition :
Type- B . 48/In
Type- C . 24/In
Type- D . 12/In
Zs ≤ 240/ 160 = 1.5
48/ 32 = 1.5Ω
240/ 48 = 5. In
32A x 5 = 160A
Mostmanufactures data-shows 3 - 5 x . In for instantaneous-disconnection .
Zs ≤ Uo /Ia .
17[SUP]th[/SUP]Edition : 2008: 2011 :
Type- B . 46/In
Type- C . 23/In
Type- D . 11.5/In
Zs ≤ Uo /Ia . Table - 41.3.
Zs ≤ 230/ 160 = 1.4375 . Round-up to 1.44Ω
46 / 32 = 1.44Ω
230 / 46 = 5. In
Type- B : > 3/In . ≤ 5.0 / In
Type- C : > 5/In . ≤ 10.0 / In
Type- D : > 10/In . ≤ 20.0 / In
If Armoured-Cable is harshly-treated the Amour-wires canbecome-displaced , twisted or stretched , leading to bulges in the sheath-material
Cablesare uniform and circular in cross-section when manufactured , but mishandlingcan result in bulges an kinks which cancause difficulties in pulling into ducts, termination at glands , as well as being unsightly , such problems can be causedby incorrect-pulling from the drum . the introduction of loop and kinks ,pulling round too tight a bend .