cliffed

-
Arms
having probs with Fire alarm.Its a sense alarm 2 wire,mcp's,detectors & sounders.
Goes into Fire mode,even when only 3 points are on circuit.
Are all their sounders compatible with the system,it's difficult to understand properly ,we have sounders,which are alarm sense,not the sounder & base ones,on their diagram.
Commissioning guy,going round in circles.
 
What happens with nothing other than the end of line device connected across the panel terminals ?
 
having probs with Fire alarm.Its a sense alarm 2 wire,mcp's,detectors & sounders.
Goes into Fire mode,even when only 3 points are on circuit.
Are all their sounders compatible with the system,it's difficult to understand properly ,we have sounders,which are alarm sense,not the sounder & base ones,on their diagram.
Commissioning guy,going round in circles.
Have you connected the bases in parallel (if using standard bases)? Both in and out should be connected to L1 in +ve and L2-ve. Not how you would connect a coventional base using in and out.
 
Split the circuit down by moving the EOL resistor, once you've narrowed it down to a section wago a detector at a time.
 
As Lee said, break the circuit down & bridge each head or call point one at a time.
I normally keep a set of short jump leads in my kit to quickly bridge things out.
 
Are you using sounder bases or have a sounder circuit? All the gear is alarmsense? EOL capacitor for detector circuits and EOL resistor for sounder circuits? If using separate sounders are they polarised?
 
Are you using sounder bases or have a sounder circuit? All the gear is alarmsense? EOL capacitor for detector circuits and EOL resistor for sounder circuits? If using separate sounders are they polarised?
No sounder circuit,all on same circuit,sounders are not base sounders,all alarm sense equipment.They are not polarity sensitive
 
In the CFP alarm sense manual, the circuit showing the alarm sense sounders shows + - at the sounders.
I just took this to indicate the sounders were polarity conscious, although it doesn't actually say this. Says to look at the manuals for each device.

Just looked on the C-tec website, your right they're not polarity conscious. In answer to your earlier question, it looks like all 5500 series sounders are compatible.
 
Last edited by a moderator:
@tazz would be the man in the know... from what I've read the sounders must be polarised they sit at a voltage between 9V-15V when quiescent and when the voltage rises above 20V the sounders activate.
 
In the CFP alarm sense manual, the circuit showing the alarm sense sounders shows + - at the sounders.
I just took this to indicate the sounders were polarity conscious, although it doesn't actually say this. Says to look at the manuals for each device.

Just looked on the C-tec website, your right they're not polarity conscious. In answer to your earlier question, it looks like all 5500 series sounders are compatible.
Thanks
 

Are both showing faulty or just 1 ?

Just read your post in reply to Lee, you mention End of line resistance ?
The manual I've got, shows 0.47uf 50v End of line Capacitors on the sense circuits.
The 6k8 resistors are for when you install conventional sounder circuits.
 
Last edited by a moderator:
Are you using Apollo Alarm Sense or are you using a 2 wire system.
If your using a 2 wire system then the sounders must be wired reverse polarity. All fire alarms weather on sounder circuits or combined zone circuit, change polarity when in alarm status, this is why bells etc have blocking diodes. Can you state the panel and exact equipment your using
 
Are you using Apollo Alarm Sense or are you using a 2 wire system.
If your using a 2 wire system then the sounders must be wired reverse polarity. All fire alarms weather on sounder circuits or combined zone circuit, change polarity when in alarm status, this is why bells etc have blocking diodes. Can you state the panel and exact equipment your using
do they have to be wired in reverse? I was reading this link which said they are operated on voltage. Apollo Fire - 55000-017APO - AlarmSense Open-Area Sounder Visual Indicator - https://www.apollo-fire.co.uk/products/range/alarmsense/sounder-visual-indicators/55000-017apo-alarmsense-open-area-sounder-visual
 
having probs with Fire alarm.Its a sense alarm 2 wire,mcp's,detectors & sounders.
Goes into Fire mode,even when only 3 points are on circuit.
Are all their sounders compatible with the system,it's difficult to understand properly ,we have sounders,which are alarm sense,not the sounder & base ones,on their diagram.
Commissioning guy,going round in circles.

From the first quote its states sense alarm 2 wire systems, this could be Fire Sense, 2 wire system...it could be Apollo Alarmsense, Could be Haes 2 wire....so once we get all the info we can go from there
 
Sorry about the waiting,all ok now,it was a loose smoke detector,not fitting to base properly.
Always the same the worst one to get at,needed scaffold to reach it.
Thanks for all your help.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
-
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Sense alarm Fire alarm
Prefix
N/A
Forum
Security Alarms, Door Entry and CCTV (Public)
Start date
Last reply date
Replies
36

Advert

Thread statistics

Created
cliffed,
Last reply from
cliffed,
Replies
36
Views
5,505

Advert

Back
Top