It's (theoretically) possible that by applying the calculations for minimum supplementary bonding csa that if it comes back in small enough (min 4mm) that your SWA armoured might be up to the job, in which case just extend the PME. Have a read of GN8.
The minimum size for a bonding conductors with a PME supply is 10mm

see Reg 544.1.1 & table 54.8

I believe this is todo with high current under PEN fault conditions and the potential for diverted neutral currents
 
It is up to the designer to assess the risks associated with a broken PEN conductor, and then put mitigation in place to reduce the risk, if the risks are unacceptable.

One way of mitigating against a broken PEN conductor risk is by making the outbuilding TT, although this is not as simple as a fix-all solution sometimes using TT can increase the risk and careful consideration should be taken into account when setting up TT systems very close to TN systems
Yes this is the scenario I am working with.
 
There is no supplementary bonding requirement. This is mainly about mitigating the risks of a broken PEN conductor.
Although you say currently you have an earth rod connected to the PME earth at the workshop, this earth rod could be counted as an extraneous conductive part, if you were to leave it this way with that earth there would need to be a minimum of a 10mm conductor connecting that earth rod to the PME MET

This is also the case for any other extraneous conductive part in either of the buildings, like water pipes etc
 
The minimum size for a bonding conductors with a PME supply is 10mm

see Reg 544.1.1 & table 54.8

I believe this is todo with high current under PEN fault conditions and the potential for diverted neutral currents
But are we discussing main bonding or supplementary??
 
Although you say currently you have an earth rod connected to the PME earth at the workshop, this earth rod could be counted as an extraneous conductive part, if you were to leave it this way with that earth there would need to be a minimum of a 10mm conductor connecting that earth rod to the PME MET

This is also the case for any other extraneous conductive part in either of the buildings, like water pipes etc

It's (theoretically) possible that by applying the calculations for minimum supplementary bonding csa that if it comes back in small enough (min 4mm) that your SWA armoured might be up to the job, in which case just extend the PME. Have a read of GN8.
Sorry I don't understand how that would protect against a broken PEN conductor?
 
There is no bonding requirement. No water pipes or anything like that in the outbuildings.
That make TT easier then, H
But are we discussing main bonding or supplementary??
Wouldn't it be main bonding
IMG_20210412_175327183_1.jpg
 
Exposed conductive parts yes, extraneous conductive parts no, unless you include the earth rod itself in that category.
In its current configuration, the earth rod is classed as an extraneous conductive part as currently the PME earth is in use at the workshop.

However you want to isolate the PME earth and change to TT, in that case the earth rod will become the earth electrode for the workshop TT system.
 

Reply to Separating PME & TT earthing for outbuildings in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
659
TNC-S main supply with 16mm swa supplying garage consumer unit from main consumer unit in house, then 4mm swa supplying pond equipment through...
Replies
36
Views
3K
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
556
Morning guys! Went to look at a consumer unit change today with a PME supply. Now, right next to this was an old BS3036 60A fused mem cutout...
Replies
2
Views
714
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock