The penny is beginning to drop I believe. Please jump in and correct me if any of my assumptions are wrong:

The disconnection times don't apply to short circuits because they don't need to - the danger is from burning up the cables, not from electrocution. Energy let through and thin conductors are more of a concern.

Minimum conductor size can be calculated for a given fault using the adiabatic, and manufacturer's data is best as it will allow the smallest conductor size. For MCBs and RCBOs, the let through energy increases with fault current.

Sound about right?
 
  • Agree
Reactions: Ian1981

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Warwickshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Short circuit disconnection times
Prefix
N/A
Forum
Electrical Wiring, Theories and Regulations
Start date
Last reply date
Replies
24

Advert

Thread statistics

Created
Pretty Mouth,
Last reply from
Pretty Mouth,
Replies
24
Views
15,127

Advert