R

Roger

Got a call today to go to a old flat as the lady was getting shocks when she was having a shower.
She explained that when she touches the tap and then the shower unit she gets a tingle and now here daughter is getting them as well.
Considering the property is a rental I was amazed to see a old rewireable fuse with some retrofit Wylex MCB put in there.No RCD ,bit of old twisted uninsulated earth wire coming up from the supply cable buried in the wall.The fuse box was not a stand alone type unit it was integral in a metal type service cabinet about 2 foot tall.
The property has an earth 0.6 (TN-S) however it only goes to power circuits,the lights have no earth and the circuit feeding the shower pump.Pulling of a cover in the cabinet revealed about 3 cables out of 8 actually had a cpc in them.
Incoming water is bonded ,but not gas to this flat and next door.Wondering around my R2 Long lead could get no continuity on any taps ,shower.
There is no supplementary bonding anywhere,lots of plastic unions so continuity if it was there is now broken.
The shower has a pump and the boiler is a conventional type with a hot cylinder upstairs.No bonding in the airing cupboard.
Now I assume she is experiencing a difference in potential which is why she is getting shocks.I could not get any shocks with the shower running and checked for any voltage present just with my volt stick and direct measurement,non existed.

But why does she get it and the previous tenant did not ?

Apart from saying the flat should really be rewired and it is not really suitable for renting i need to provide a detailed explanation as to what is going on and why it has not happened previously.

If i upgraded and put in main bonding to services and run upstairs to bathroom from MET,also supplementary bonding in bathroom under bath and sink and airing cupboard would that fix it.

She has just signed for 6 months so not really practical to rewire now,if he actually wants to go ahead.
Any help greatly received
 
Is there a metal waste to the bath? This could be bringing in an earth potential. Immediate solution would be to bond the bathroom and get an rcd on the place.
 
No metal waste ,all plastic.Having a look around outside bloody wires and cables everywhere.Outside patio ,decking on a flat roof all lights in twin and earth !.Old telephone wires all over the place.
 
I guess i could split the tails and like you say RCD the whole board.Nuisance tripping might be a problem as she sent me a text saying that the lights dimmers where staying on !
A right can of worms.
Do you think i am going down the right route and it is a potential difference that causes the shocks ?
Cheers
 
Almost certainly, it's just a case of finding out where thepotentials are coming from.

There was a case a few years ago where the foil on the back of the plaster board was the culprit, the lady had had some handrails fitted for her safety in the shower and they nearly killed her.

You could be there some time
 
First thing is I'd want to clarify the following with them. Is it that they are touching the tap and the shower at the same time, or first one then the other?
 
I am sure she said both,why ? although during all conversation she says its the shower head.

Under the bath the pump is housed and is feed from a fused spur (I can see it but whether i can get to it is a different matter to check it has a intention of having an earth) which goes back to probably a JB under the tiled floor ,then back to a 15amp rewireable fuse at the old sort of CU.The hot and cold feeds come up through the floor and then plastic speedfit and then back to copper for a bit then buried in wall is copper feeds to the shower valve.

I had thought that the shower pump might be causing a problem but they are so well insulated and with the lack of bonding i have gone down that route.The bath Tap is not pumped ,the pump only works with the shower.
Thanks
 
I am sure she said both,why ? although during all conversation she says its the shower head.

If they are touching the tap and shower at the same time then it's a most likely a live potential difference you're tracking down. If they're touching the tap followed by the shower (after breaking contact with the tap) then it may only be a static build up on the shower. Which might go someway towards explaining the "only happens now" bit.

If it's definately a tingle and not a sharp shock then it may only then be something around 50V so using a volt stick may not register the PD. They have their uses but not for this IMHO.

Is the shower an electric shower or just a boost pump fed mixer valve?
 
I wouldn't offer to stick an rcd on the front of the installation until i had put an earth leakage clamp meter on everything to see if it is going to hold. You could be opening a big can of worms with the time honoured phrase of "it was working before" bouncing off your eardrums.

It sounds from your description that bonding everything in the bathroom should get all the metal work at the same potential and so stop tingles.
 
  • Like
Reactions: 1 person
If they are touching the tap and shower at the same time then it's a most likely a live potential difference you're tracking down. If they're touching the tap followed by the shower (after breaking contact with the tap) then it may only be a static build up on the shower. Which might go someway towards explaining the "only happens now" bit.

If it's definately a tingle and not a sharp shock then it may only then be something around 50V so using a volt stick may not register the PD. They have their uses but not for this IMHO.

Is the shower an electric shower or just a boost pump fed mixer valve?

its just a shower booster pump to fed a mixer valve.

I am trying to jiggle a few things around so i can get back there tomorrow to carry out some work on the earthing and bonding.
I need to speak to the owner of the other flat as when i opened the service box for the gas meters ,one was very smelly.See what it smells like tomorrow.
Rusty old gas main,get me wire brush out to get a good connection.
 
.

If it's definately a tingle and not a sharp shock then it may only then be something around 50V so using a volt stick may not register the PD. They have their uses but not for this IMHO.

?

Totally agree a volt stick is not for this job. The voltage you could be looking for though is likely to be more in the order of 1 or 2 volts as as a wet body could have a resistance in the order of 1000Ω and a tingle would likely be around 1 or 2 mA.

So V = I x R, = 0.002A x 1000Ω = 2V :)
 
Totally agree a volt stick is not for this job. The voltage you could be looking for though is likely to be more in the order of 1 or 2 volts as as a wet body could have a resistance in the order of 1000Ω and a tingle would likely be around 1 or 2 mA.

So V = I x R, = 0.002A x 1000Ω = 2V :)
I wouldn't suggest he does his testing wet :p

I doubt you'd get a resistance that low, but agreed that could in theory be a worse case.

Following that logic though the voltage you could be looking for could be as high as 230-2=228V to get a PD of 2V. Depending on what the potential is between.
 
if i were you i would suggest (and put it in writing)that a periodic inspection is carried out, she should of had one of these when she moved in from landlord.if the wiring is that bad i would not try to fault find in fact i would tell her NOT to use bath until full testing of all circuits and logged.
being the last electrician on site you are responsible and god forbid tingles off of taps become lethal you might have a lot of explaining to do.
 
  • Like
Reactions: 1 person
I guess one of our assumptions here is that the bath is forming the return part of the circuit. It could either be at (or around 0V) or that could be introducing the potential to give you around 2V difference (so could even be a fault somewhere else completely).
 
I wouldn't suggest he does his testing wet :p

You mean you don't carry your speedos in your tool kit :p

I doubt you'd get a resistance that low, but agreed that could in theory be a worse case.
If the lady is wet and standing in the bath not unusual for body resistance to fall to 1000 Ω (even wiki says so)

Following that logic though the voltage you could be looking for could be as high as 230-2=228V to get a PD of 2V. Depending on what the potential is between.
:confused: a voltage is the difference in potential between two points. Yes if you are in contact between 2 points at 300V and 228V you feel the effects of a 2V potential difference - but the moment one hand touches something approaching earth potential you are going to feel a lot more lol :)
 
you have said the install looks old i would insist that the installation be given a periodic , i had a call once infact the call i had i has been used on several articles one in wiring matters and was an old install rented property , what basically happened i got a call getting shocks of off metal work in the house , went there thinking static , only to find a woman in her dressing gown sat on the floor shaking her kids crying ,quite stressfull to see ,asking what had happend the lady had started to run a bath , during the time the fault had occoured the bath had filled with very hot water due to a faulty tank stat to when she went to get in the bath she felt a tingle and though it was just because the tap was hot , it wasnt untill she put her leg into the bath that and ended across the bathroom she realised it was live switching off the power and carrying out some tests i discovered a fault in the immersion heater 3036 rewireable fuses , the insulation had broken down on the cable causing a short between live and earth , but instead of blowing the fuse the live blew the earth connection and welded its self to the metal work of the heater this caused every part of the water system had become live cast iron bath was live even the flush handle of the toilet was live , although the bonding had been installed it had never been connected if it had it would have blown the fuse the lady was very lucky , i made the install safe and next day carried out a periodic inspection , what you have here may not be anything like what i discovered and the woman too but you cant be to sure , so inspect the shower and recommend a PIR at the end of the day doesnt matter who they are the land lords have a duty of care , print off the ESC 's landlord guide to electricicty and give it to them but make sure you test the shower top to bottom and check the bonding some thing so simple could save a life
 
  • Like
Reactions: 1 person
"I wouldn't suggest he does his testing wet" :p

I'll take me towel !

I did advise her not to use the bath and shower until it is rectified,got 2 kids in there as well.Like you say i touched it last.
The whole place is really shabby and very old.God only knows what else is on the shower circuit and where it is taken from.I''ll give him a day rate and go from there.She's paid 6 months up front so the landlords feeling a bit flush.
Just hope the earthing and bonding solves it.
I ask what he has done about the periodic,I know he has had the gas checked as that bloke recommended me.Either way i will put it in writing so me bum is covered.
Cheers
 
  • Like
Reactions: 1 person
:confused: a voltage is the difference in potential between two points. Yes if you are in contact between 2 points at 300V and 228V you feel the effects of a 2V potential difference - but the moment one hand touches something approaching earth potential you are going to feel a lot more lol :)

Agreed. Think I'd best pack some for future use ;)

So we need options ... how else can we be getting around 2V between a tap and shower head?

Any potentially faulty SELV in the bathroom?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shower Electric shocks but not everyone
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
59
Unsolved
--

Advert

Thread statistics

Created
Roger,
Last reply from
mickys86,
Replies
59
Views
14,998

Advert