Hi had a 45amp shower pull cord switch melt on me so replaced it with a 50amp one did it all correctly but no joy and the switch doesn't come on or light up. Is it possible the shower itself has gone aswell.

Please help!
 
Hi had a 45amp shower pull cord switch melt on me so replaced it with a 50amp one did it all correctly but no joy and the switch doesn't come on or light up. Is it possible the shower itself has gone aswell.

Please help!
Is it possible the original burnout tripped something in the CU?
 
Hi had a 45amp shower pull cord switch melt on me so replaced it with a 50amp one did it all correctly but no joy and the switch doesn't come on or light up. Is it possible the shower itself has gone aswell.
i bet you not correctly put the cables in , has the fuse dropped or fuse blown .
 
Or possibly put burnt cable into the terminals and so not making a good connection? Did you strip the insulation back to good clean copper?
 
  • Like
Reactions: DPG
Hi - good advice above - and I’d just add that shower circuit is high power well able to do damage if all is not well so you’ve any doubts please get help :) .
 
  • Like
  • Agree
Reactions: DPG and Pete999
If the burnt out switch was put in at the same time as the shower, I’d check the terminations in the shower as well.

You can’t go far wrong with a switch. There’s only L an N IN.... from the mains, and L and N OUT to the shower.
Double check them.
 
  • Like
Reactions: DPG
20201126_114705.jpg
 
  • Dislike
Reactions: suffolkspark
Left is load and right is supply I double checked by pulling on cable connected to the shower and still no power
 
The switch appears to be miswired. You have a black neutral cable on the right wired to a connection which is marked L for live. Also, way too much copper showing on the leftmost red (Live) cable, and some damaged insulation on the leftmost neutral (which may be to the wrong terminal anyway). I think you have been lucky on this occasion - you could have faced a short circuit which would trip a breaker or blow a fuse.

The most likely reason that the switch failed the last time is that the connections were either too loose or the cables were poorly cut and terminated. As poor connections are a fire hazard, please get a competent person such as an electrician in to do this for you.
 
Last edited:
I had a case last year where I replaced a burnt-out pull cord isolator like this one. After removing the "worked" (brittle) bits of damaged cable and made good terminations on a new switch, I did an R1+R2 at the shower to confirm everything was spot on, and I got poor (high) readings.

It turned out there was another 45A DP isolator, a plate switch, downstairs in the service cupboard near the consumer unit. This had also been poorly terminated and was burnt out, and also needed replacing.

It reminded me of the importance of testing, even for a relatively simple "straight swap" maintenance job.
 
  • Agree
Reactions: Pete999 and Zerax
and the way those sheaths are split is R.A.F.
Agree the installer had nil sense of cable dressing to make life easier for him/herself
 
  • Like
Reactions: loz2754

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Shower pull cord switch melted new one not working.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11

Advert

Thread statistics

Created
apjmoore1990@g,
Last reply from
Pete999,
Replies
11
Views
11,671

Advert