I am trying to run it fixed as it should be: with both rotor ends inserted into both bearings.
Thanks Mate, needed to ask, seen some stupid stiff in my time, not in any way that what you have done is stupid,
 
  • Like
Reactions: Christopher
I am trying to fix a single phase ac motor but need some help. When powered on and put off load, motor humms but doesnt rotate, its sort of magnetically locked because even trying to rotate by hand it very hard to turn (motor was removed from housing and therefore I have stator and rotor exposed)

When switched off, rotor turns freely and smoothly by hand, therefore bearings are not an issue.
Motor is a capacitor run. Checked capacitor and both windings, all looks fine (see image attached). Coils ohmage measured was 15 and 40 ohms and capacitor reads 10microF OK.

Can someone please help what could be the problem? Thanks!

Hi
Did you solve the issue, how
I have the same issue in motor
 
I am trying to fix a single phase ac motor but need some help. When powered on and put off load, motor humms but doesnt rotate, its sort of magnetically locked because even trying to rotate by hand it very hard to turn (motor was removed from housing and therefore I have stator and rotor exposed)

When switched off, rotor turns freely and smoothly by hand, therefore bearings are not an issue.
Motor is a capacitor run. Checked capacitor and both windings, all looks fine (see image attached). Coils ohmage measured was 15 and 40 ohms and capacitor reads 10microF OK.

Can someone please help what could be the problem? Thanks!
Centrifugal switch gone U/S
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Single Phase AC MOTOR stuck
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
22

Advert

Thread statistics

Created
Christopher,
Last reply from
Petej999,
Replies
22
Views
10,777

Advert