This is a construction site supply someone has put in at a mates new build site, I think there is a non compliance with the regs, see if you all agree or am I being picky?
IMG_20160428_184109.jpg
 
not sure what you're not sure about.
 
  • Like
Reactions: 1 person
External meter box, IP rating not met when the door is open due to flexes wedging it open????
 
Good job you lot don't come to me for advice, I misread the regs, was looking at sockets in excess of 16amp and these are clearly sockets rated at 13amps. Numpty!:-)
 
I'd even flicked through 70x for construction sites and I couldn't find anything haha
 
  • Like
Reactions: 1 person
They are only rated to 20amps, even though a total load of 26 amps is quite possible.
 
plastic sockets with bob the builder around? that's a mistake. and the DB should be fitted with 3036 fuses so he can substitute nails.
 
Last edited:
They are only rated to 20amps, even though a total load of 26 amps is quite possible.

If they are rated to 20 amps then I was correct!? Look at reg 704.511.1 states that all sockets with a rated current equal to or greater than 16amp on a construction site supply shall be compliant with BS EN 60309-2

BS EN 61439-4.jpg
Should a temp supply have these or as previously stated am I being picky, would be good to see a builder trying to plug a 13amp plug into one of these!?:-)
 
Last edited by a moderator:
Sorry forget that as it is irrelevant. BS1363 13 amp sockets is what they are. Although the doubles are rated to handle 20amps when a total of 26 is unlikely but possible.
 
so what was the outcome? what was the mistake?
 
Sorry no mistake, was me being a numpty, I thought the twin sockets were rated at 16amps or above and they are rated at 13amps.


so if they were rated at 16amps, would that have been non compliant?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Spot The Mistake?
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
15

Thread Tags

Tags Tags
mistake

Advert

Thread statistics

Created
rolyberkin,
Last reply from
rolyberkin,
Replies
15
Views
261

Advert