If you mean can you wire an exterior light fed from a FCU which is part of a RFC then the answer is yes providing you don't exceed the rating of the fuse in the FCU or the new wiring
your outside light would only need RCD protection for the cable if buried <50mm deep in the wall. however, i'd recommend fitting RCD to the RFC to give the customer additional protection on the sockets.