job came in today. granny flat already has 32A ring and 6A lighting. cust. has had a shower room built on. will have a 9.5kW shower and 5 downlighters. no problems there, and room on house CU to fit MCB and RCD. problem is, the sub main is fed with 6mm SWA. obviously inadequate. cust is OK with upgrading SWA.
BRB says 10mmSWA buried and in free air can carry 60A. this is ( taking diversity into account ) just about enough. 16mm would be ideal, but a pain to install due to bend radius and glanding. anyone think 10mm will do? or should i go for 16mm
 
i would be thinking 16's if you mean a sub-main for separate board in granny flat

maybe i'm misunderstanding -but i wouldn't rcd the sub-main if that's what you intend
 
the feed is to an existing CU in flat. i can feed from either RCD in house board, or put the RCD protection in the flat. The house board at the moment ha 6 circuits, all on one RCD ( 16th Ed. Split Board) but can be made into Twin RCD board. existing 6mm to flat was from RCD protected MCB in main CU, but disconnected wthen building mods, started on flat.
 
not that familiar with uk rules but

i think the swa sub-main means no rcd required on it -so it should be avoided as it could create a hazard in the bathroom esp. for elderly
 
SWA don't need RCD as its part surface , part buried. The " flat" is just one room with shower room attached. RCD is essential. either one end or the other.( socket, shower , and buried cable in walls) i've got it all sorted except the actual size of SWA. My loading with diversity applied is 56A which is just about the limit for 10mm. My plan so far is to upgrade the main CU to 2 RCDs as there is room to do this, and feed the SWA from the protected side of the board, replacing the existing 32AMCB with either 50A or 63A. just need to decide on 10mm or 16mm SWA
 
whats the existing load on the 100a fuse in the house with diversity applied?,what is the lenght of run?
got to check house load with diversity yet, it's not high. SWA run is 15m. surface cleats and underground.
 
exactly my thoughts. the only high load is the shower. no heating, no appliances, just will be TV, kettle, lights etc. i think 10mm is adequate as shower is only occassional use for 5 - 10 mins.
 
That's the thing I would think, over the lifetime of the cable it won't be drawing all of that at once so you should be able to get away with it.
 
SWA don't need RCD as its part surface , part buried. The " flat" is just one room with shower room attached. RCD is essential. either one end or the other.( socket, shower , and buried cable in walls) i've got it all sorted except the actual size of SWA. My loading with diversity applied is 56A which is just about the limit for 10mm. My plan so far is to upgrade the main CU to 2 RCDs as there is room to do this, and feed the SWA from the protected side of the board, replacing the existing 32AMCB with either 50A or 63A. just need to decide on 10mm or 16mm SWA


yes- on the sub-board

30ma is a hazard on the main DB in this case
 
I'd still go 16, what if the customer in the future wants a small electric heater in there or something like that? Unless there is already a gas heater/ central heating in the building.

:)
 
central heatin piped fromn house. i could even down rate the ring main to 16 or 20A MCB. it's one of those borderline cases. just that 16 will be a pig.
 
What does this mean?


i do get a bit twisted with the uk rules(not too familiar)

anyhow in principle when fitting rcd's avoid causing a nuisance or hazard-so here in this granny flat job

sub-main is swa so no rcd required
if lights require 30ma protection rcbo them so a fault on the ring main doesn't knock out the lights when an elderly person is showering for example-that is the way i would do it anyhow

not much extra cost involved

unless i'm mistaken(could well be!)
 
Last edited by a moderator:

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
Supporter
~
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
sub main feed
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
21
Unsolved
--

Thread Tags

Advert

Thread statistics

Created
telectrix,
Last reply from
telectrix,
Replies
21
Views
4,153

Advert