With this type of question there are so many ways it can be done. From really cheap (tapping into existing house circuit, use 2.5mm SWA to shed....) to spending a bit more and having something that you can expand on in the future.
Personally I would go with 4mm SWA back to house CU. Small 4 way CU in shed. ( room for future stuff, like garden lights and instantaneous inflatable dolls that scare off burglars.... ) One RCD on shed CU (as mine has only tripped once in about 12 years) and MCB in house CU. If I had a bit extra to spend then go with RCBO's in garage CU.
 
  • Like
Reactions: 2 people
Just put an upfront rcd in shed to cover any future add ons, what's the point in shelling out extra for rcbos?

Spend the extra on a larger size swa cable
 
Yes it has .... once or twice - along with bathroom lights & extractor fans, RCDs tripping after a re-wire, and "Why does my landing light not work since I changed the light fitting in the hall?" .. etc. etc ..... not to mention "Does this gas pipe need bonding?"

The list goes on ad nauseam.
smiley-sick029.gif
 
I personally would run a 4/6mm2 fed from 32A supply to a little CU in the shed (CU with 30mA RCD as main switch, and option to put 6A and 20A radial in . I would make the CU a TT system (earth rod) just so you dont have any nuisance tripping from the house, just in case they put outside lights. (the amount of times i get a phone call saying the RCD in their house wont stay on because water has got into one of their outside lights.

hope it helps
 
Cant understand why people are saying that you can tap a cable straight out the back of a socket especially if its a pme installation in the house. I do agree that taking the swa back to the mains rather than joining it is a good idea but one join in an adaptable box Is not the end of the world. Also you have to consider how the cable from the mains to the shed is being installed, if it is surfaced trunked then it doesnt necessarily have to go through an rcd but if it is buried in the wall in twin and earth then it must be covered by a 30ma rcd or rcbo. If the installation is pme I would recommend a minimum of a 4mm 2 core swa to the shed then I would cut the armouring off in the shed and install a earth stake on the shed. If the cable therefore from the house to the shed is covered by and rcd or rcbo then just install a main sw plus mcbs in a small shed consumer unit.
 
  • Like
Reactions: 1 person
Or just a bit of 2.5mm 3 core swa terminated into metal clad socket in the shed then from there either more sockets or you could put a sfcu as the light switch and then a fcu for the alarm. If you do this you could technically come off a socket in the house via a 13a spur. Just a thought...

You could even put one of them wind turbine thingies on the roof and save the bother of running a length of cable from the hoose.
 
  • Like
Reactions: 3 people
Cant understand why people are saying that you can tap a cable straight out the back of a socket especially if its a pme installation in the house. I do agree that taking the swa back to the mains rather than joining it is a good idea but one join in an adaptable box Is not the end of the world. Also you have to consider how the cable from the mains to the shed is being installed, if it is surfaced trunked then it doesnt necessarily have to go through an rcd but if it is buried in the wall in twin and earth then it must be covered by a 30ma rcd or rcbo. If the installation is pme I would recommend a minimum of a 4mm 2 core swa to the shed then I would cut the armouring off in the shed and install a earth stake on the shed. If the cable therefore from the house to the shed is covered by and rcd or rcbo then just install a main sw plus mcbs in a small shed consumer unit.

If there are no pipes or equipotential parts entering the shed then there is no need for the earth rod at all, whether its TNS or TNCS!!! And I think the op has already suggested running the submain in SWA, maybe with T&E in trunking inside the house, so no need to RCD/RCBO at the house end. This would be a right pain in the back side, every time it tripped, you would need to go into the house and reset it, instead of just into the shed.

There are allot of variables to consider with this install and the OP hasn't given enough info!
 
Yes it has .... once or twice - along with bathroom lights & extractor fans, RCDs tripping after a re-wire, and "Why does my landing light not work since I changed the light fitting in the hall?" .. etc. etc ..... not to mention "Does this gas pipe need bonding?"
Well does it? :)
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
SWA to shed - agree with my proposal?
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
sparky05084,
Last reply from
spadge47,
Replies
33
Views
4,088

Advert