Just a quick question can you put a switched fused spur in a bathroom outside the zones 1 & 2.
Cheers
 
Personally I would put it outside the bathroom for safetys sake.
 
must be dodgy info here... unless it's selv or pelv... you can't put a sw/fused spur within 3 m of zone 1?...

check regs 701.512.3 and 701.55
 
I looked at a job the other day the combi boiler was in the bathroom with a switch fused spur next to it. my first reaction was no switch's in a bathroom, but you see towel rails all the time with switch fused spur on them in a bathroom. But then why are fan isolator either pull cord or outside the bathroom.
 
must be dodgy info here... unless it's selv or pelv... you can't put a sw/fused spur within 3 m of zone 1?...

check regs 701.512.3 and 701.55


230v socket outlets are permitted 3m beyond the horizontal outside edge of zone 1. 701.512.3

Switched fused spurs are permitted outside the zones.
 