N
NeonSparks
just moved an mcb to rcd side of board and now a lighting radial on NON rcd side trips rcd...any ideas? I'lm sure i have moved correct wires.
Can't you put both lighting circuits on rcd side and note on cu about borrowed neutral if customer doesn't want to pay for fault finding?
If two circuits are sharing a neutral you can move both the circuits to the RCD side of the board along with their neutral(s) and peace and harmony should be restored.![]()
Agree both would have to be on same mcb as you have stated.
Why's this? If both circuits share the same neutral, by putting both MCB's on the same neutral bar (and same RCD) then surely it's the same thing?
To have upstairs on 1 mcb and downstairs on a different MCB (albiet on the same RCD), would that not be better than powering 2 circuits through the same MCB?
No because if one mcb is isolated to work on a fitting then the borrowed neutral will become live if the other circuit is not also disconnected.
The difference there is that if you isolate one circuit to work on it and the other circuit is still on the circuit that is still on has a neutral connected to the board and therefore a return path for te current. In the case of a borrowed neutral when you split the circuit at the borrowed neutral you are breaking the return path to the board therefore that neutral will be live.I know your right, but I can't get it straight in my head.
Lets say there was no borrowed neutral and both circuits wired correctly, both MCB's connected to the same RCD and same neutral bar, are the neutrals still not connected together, only this time at the board rather than at the light fitting?
Well said Hawk couldn't get it into words myself, the beer has taken over.
Sorry it wasn't meant to be taken as good advice, hence the smile. I'll wrap it in [Sarcastic][/SARCASTIC]tags next time.i would not say peace and harmony are restored by leaving a borrowed neutral as this is dangerous. surely not great advice!!
think it could be put more simply. all are talking of a borrowed neutral, but i would rather call it a borrowed live. the landing light is upstairs, so is on the upstairs lighting, but only as as regards the neutral, but has " borrowed " the live from downstairs. therefore, if you isolate the upstairs, you still have a live from downstairs to the landing light.