N
NeonSparks
just moved an mcb to rcd side of board and now a lighting radial on NON rcd side trips rcd...any ideas? I'lm sure i have moved correct wires.
Sounds like a borrowed neutral.
What circuit was on the mcb that you moved?
Have you moved the neutrals onto the correct bars in the cu or else it could be a borrowed neutral between the circuit you moved and the lighting circuit.
I would guess that the neutral as been borrowed for the two way switching for the landing.
Absolutely the landing light is probably on the downstairs lighting circuit due to the 2 way switching but the neutral will be taken from the upstairs circuit.
If two circuits are sharing a neutral you can move both the circuits to the RCD side of the board along with their neutral(s) and peace and harmony should be restored. :-)
Tripping rcd
Australia
NeonSparks,
Ponty Massive,