As already said the Earth rod is connected before the Consumer unit so all the rod is doing is adding to the PME earthing.

If the Rod was connected to the earth bar in the Consumer unit and penetrated the Neutral, it would no longer be a TNC-S as there would be no Separation from the earth bar.
Thank you, getting there.
So this is a TN-S system but where the installation’s earth has been connected to the “first” earth in the PME chain.

IMG_2857.jpeg
 
current will always take the path of least resistance which is most unlikely to be your new earth rod.
Probably should have said 'most' as the earth rod having a significantly higher resistance, the current would be insignificant (probably) but this is all hyperthetical!
 
  • Like
Reactions: Tom256
  • Agree
Reactions: DefyG
That is not TN-S. Do you understand why?
Hmm, for TN-S the installation earth is directly connected to the source earth (usually via the DNO’s supply cable’s metal sheath, this is not the case so not TN-S.
For TN-C-S the separate bit is missing
So yes not TN-S, but not TN-C-S since the S is missing.
By process of elimination it’s a TN-C, in the book I read.
“TN-C is not generally permitted in the UK.”
Ok time to read up on TN-C.
 
Hmm, for TN-S the installation earth is directly connected to the source earth (usually via the DNO’s supply cable’s metal sheath, this is not the case so not TN-S.
For TN-C-S the separate bit is missing
So yes not TN-S, but not TN-C-S since the S is missing.
By process of elimination it’s a TN-C, in the book I read.
“TN-C is not generally permitted in the UK.”
Ok time to read up on TN-C.
Consider the 'S' in TN-C-S. What part of the electrical system does this aspect apply to? Where do the neutral and the protective earth become separated never again to come together?
 
Last edited:
Consider the 'S' in TN-C-S. What part of the electrical system does this aspect apply to? Where do the neutral and the protective earth become separated never again to come together?
To help with your consideration of this. Using your diagram in post #21.
The earth point on that 3rd electrode (closest to the installation) was moved along by some form of pixie a tad and was now at the origin of the customers installation.
 
Last edited:
Hmm, for TN-S the installation earth is directly connected to the source earth (usually via the DNO’s supply cable’s metal sheath, this is not the case so not TN-S.
For TN-C-S the separate bit is missing
So yes not TN-S, but not TN-C-S since the S is missing.
By process of elimination it’s a TN-C, in the book I read.
“TN-C is not generally permitted in the UK.”
Ok time to read up on TN-C.

For it to be TT earthing, you would have to have the ROD connected to the earth bar in the consumer unit.

The PEN would be isolated from that consumer unit.
 
What part of the electrical system does this aspect apply to?
S refers to the installation side, whereby the earth and neutral returns are “Separate” on this side.
Where do the neutral and the protective earth become separated never again to come together?
The neutral and earth separate at the intake of the installation.

Just searched youtube and found a video for you that may help with your understanding. I have not watched it through but from my quick scan through it covers one of the points you have raised:

View: https://www.youtube.com/watch?v=z7han_twcnw

This was interesting. The PEN fault at neighbor 2 meant that their neutral was returning through their earth, into the metal services, into neighbor 1’s and then into neighbor 1’s earth-neutral link.
When neighbor 1 disconnected their earth neighbor 2’s electrics stopped, with the added drama of this energizing everything connected to the earth systems of both neighbors.
To help with your consideration of this. Using your diagram in post #21.
The earth point on that 3rd electrode (closest to the installation) was moved along by some form of pixie a tad and was now at the origin of the customers installation.
I’m still thinking about what kind of earth system it would be. I think that a TT that is connected back to a TN-C-S (e.g. via some metal pipe work that’s been earthed by both systems) is an extension of that TN-C-S.

After reading all this my question becomes, what happens if the earth electrode in what is intended to be a TT system connects/is not sufficiently insulated from the CNE.
The CNE is used by other installations (e.g. other houses) as part of their TN-C-S systems.
 
Last edited:
I’m still thinking about what kind of earth system it would be. I think that a TT that is connected back to a TN-C-S (e.g. via some metal pipe work that’s been earthed by both systems) is an extension of that TN-C-S.
Its still a TT.
 
Last edited:
After reading all this my question becomes, what happens if the earth electrode in what is intended to be a TT system connects/is not sufficiently insulated from the CNE.
The CNE is used by other installations (e.g. other houses) as part of their TN-C-S systems.
It may prevent a protective device from operating.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Hakuhou

Trainee
Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Trainee Electrician

Thread Information

Title
TT undetectable PEN fault
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
33

Advert

Thread statistics

Created
Hakuhou,
Last reply from
buzzlightyear,
Replies
33
Views
1,805

Advert