Thank you, getting there.As already said the Earth rod is connected before the Consumer unit so all the rod is doing is adding to the PME earthing.
If the Rod was connected to the earth bar in the Consumer unit and penetrated the Neutral, it would no longer be a TNC-S as there would be no Separation from the earth bar.
So this is a TN-S system but where the installation’s earth has been connected to the “first” earth in the PME chain.