Macsamillion
Thanks. It's scary to think that the voltage is induced, but this is what I have come to believe through checks. I did try to check IR between conduit wires but my tester let me down before I got going.with a LED lamp, it's not unusual for it to glow dimly when off, as a result of capacitive coupling between the live and switched live. With 2 way switching, there's likely to more chance for capacitive coupling, because there's likely to be more switched live and permanent live running alongside each other.
In your case, the problem is likely to be good old fashioned leakage, because the insulation of the wires is breaking down.
A 500V IR test between the wires would confirm, but as said above, there really shouldn't be VIR cable still in use.