stuart mills

I have applied for a 15kva single phase supply on my site. There is a 11kV 3 phase service in the verge.
The soil is light/sandy with crops/grass.
Western Power have quoted £27,000 for a pole mounted transformer installation saying that I need to dig 135m for 3x70mm2 earth for the 11kV and 120m trench for 3x70mm2 for the LV. This equates to about 1/2 mile of copper! 780 meters!
They have not carried out soil conductivity tests.
Other supplies in the area are a good distance away as it is countryside but they seem to have an earth rod. They say that I can pay them £350 to send someone out with test equipment if I want to pay them to be able to justify their quote. They say their records show the ground as sandstone. I can't imagine what would happen if our site was only large enough for a single dwelling.
Any opinions or advise would be greatly appreciated.
Regards Stuart
 
Seems about right compared to other quotes, usually not less than £17000 for a remote single phase single dwelling supply.

The others are existing supplies presumably, which wouldn't have been installed to todays standards.

Have you had a quote for water yet, or is it a spring / borehole?
 
Seems about right compared to other quotes, usually not less than £17000 for a remote single phase single dwelling supply.

The others are existing supplies presumably, which wouldn't have been installed to todays standards.

Have you had a quote for water yet, or is it a spring / borehole?
Thanx for the reply, given that the 11kV is right next to site I am surprised at the quote. The price is high due to 1/2 mile of earth cable being required allegedly. Water is 3k.
 
Earthing can be difficult and costly especially for transformers as the readings required are normally very low.

Have you been given a breakdown of the quote?
 
These guys are never cheap. Can you ask for a break down of the costs and ask if any of it is contestable? Sometimes they will let you do some of the work using your own contractor to their standards. They always make the final connection. At the very least I would ask them if you could do the excavations, perhaps also supply and install the earthing.
 
  • Agree
Reactions: StephenRowley
These guys are never cheap. Can you ask for a break down of the costs and ask if any of it is contestable? Sometimes they will let you do some of the work using your own contractor to their standards. They always make the final connection. At the very least I would ask them if you could do the excavations, perhaps also supply and install the earthing.
Thanx for the reply. The quote excludes excavation that I have agreed to carry out, it just seems that their stated requirement of 780 meters of earth is ridiculously long.
 
My understanding is a lot of this stuff is contestable works and you dont have to use western power. it may pay to get some other quotes. if these are substantially lower use them, additionally a lower quote may get western power to lower the price.
 
Talk to them, it sounds like they are quoting for worst case. Normally they are looking for less than 40 ohms for the HV earth and less than 20 ohms for the LV. with at least 8 meters separation between them.
 
Talk to them, it sounds like they are quoting for worst case. Normally they are looking for less than 40 ohms for the HV earth and less than 20 ohms for the LV. with at least 8 meters separation between them.
Thank you for the reply, they have said that if they discover the 780 m of earth is deemed over the top when on site that they will refund but I am afraid that once I accept the quote I will not see any cost cutting.
 
It may be possible to lay some of the LV earth in the same track as the LV cables which may save a bit. How many houses?
 
It may be possible to lay some of the LV earth in the same track as the LV cables which may save a bit. How many houses?
Hi, thank you for replying, it is only for a site cabin for a quad bike track but we tend to get diesel or generators taken so I wanted a permanent supply. The LV run is only 6m.
 
Talk to them, it sounds like they are quoting for worst case. Normally they are looking for less than 40 ohms for the HV earth and less than 20 ohms for the LV. with at least 8 meters separation between them.
I've never seen one so high? Our spec is always at least below 10 ohms when we do these type of jobs
 
Thanx for the reply, given that the 11kV is right next to site I am surprised at the quote. The price is high due to 1/2 mile of earth cable being required allegedly. Water is 3k.
do you know to install a supply like that comes with a high price E.G. engineers equipment and all the sundries .
 
A built in genny may be a better solution, very hard to steal !
 
Why dont you have an off grid set up if it’s only for a portacabin? What is your likely load to be in the property?
 
Why dont you have an off grid set up if it’s only for a portacabin? What is your likely load to be in the property?

Sounds like they already do that, but the equipment keeps getting nicked.
 
Hi,you would be as well,to go down the alternative quote route.
I cannot imagine that the supply and water,is planned solely for the quad track,and the investment,may be justified by an increase in the assets worth,and any future plans.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Western Power massive supply fee
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18

Advert

Thread statistics

Created
stuart mills,
Last reply from
plugsandsparks,
Replies
18
Views
2,539

Advert