If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)
Looking at this job, I haven’t touched anything yet so any faults you find are nothing to do with me.

The top switched fuse feeds a CU in the house.

The bottom one is old and the customer would like to use it for another CU in an out building. A 16mm SWA has been run to the box.

Now I am struggling how to think about terminating it all and doing a neat job.

First thing would be to seal the hole and stop the snails.

I’m not sure about using the old switch fuse as the holes cut out on the top don’t look right and is a cover missing? I have seen new ones of these available from wholesalers so that could be an option. But could be a tight squeeze.

There is room for a second meter box along side which could house the 2 switches or just the the second one and then would just need to worry about getting meter tails through.

Would like to hear your thoughts so I can come up with a plan.

Thanks.

0246D930-3D0E-4A53-8CB7-5C68E84CBF50.jpeg
 
For me another meter box for the 2 switch fuses is the best option.
 
  • Useful
Reactions: Andy5678
Yes and then have the metallic fused switches. Not sure about running tails from box to box. Not sure what’s the largest diamater of conduit/copex available to fit 2 x 25mm tails plus 16mm earth.
 
I think it might a split concentric cable? It’s defiantly not SWA. Sleeved for double insulation possibly, not sure didn’t want to poke about too much at it.
 
Run some large ducting between the boxes. 50mm should do it.
 
  • Useful
Reactions: Andy5678
They must have been recently to fit the smart meter, take it nothing was said about the state of it.
 
I'd get rid of both the switches and install DP isolator switches. Power the out building the usual way. I don't see the purpose of multiple cut out fuses.
 
Cid, i would prefer to keep the fuses. Not going into why as want to keep the discussion on the set up.
 
Why is the bottom switch not used? Could it be defective (possibly damp / moisture ingress?) and they’ve just left it place and fitted new one above?
I know you’d rather keep the fused switches ,but Could you not install a small DB with a main switch and two 63amp mcbs, so you’ve got isolation and overcurrent protection for both out going cables and you don’t have faff on with Henley blocks or try to link those old fused switches together?
 
  • Informative
Reactions: Robster694
I prefer switch fuses for discrimination.
 
I prefer switch fuses for discrimination.
Was just thinking out aloud with that idea, was thinking of the tidiest way to do it, but of course Zs readings etc would have to be taken into account for suitability of protective device.
 
KEV thought about doing that but discrimination with MCBs may not be good with the main house being on it too, I agree it would be a neat way of doing it.
 
Do cgd do a double fuse version of their switchfuse assembly?
Wondering if you could have a single enclosure with 1 main switch and then 2 fuse holders supplying each submain? Like the 63A breaker approach, but retaining discrimination.
 
  • Creative
Reactions: JOURNEYMAN
They must have been recently to fit the smart meter, take it nothing was said about the state of it.

Nothing would be said,as a vast number of the people fitting them,would not be aware of a problem,if there were a nest of snakes at the bottom,and the top was on fire...
 
  • Agree
Reactions: Baddegg
Nothing would be said,as a vast number of the people fitting them,would not be aware of a problem,if there were a nest of snakes at the bottom,and the top was on fire...

Well to be fair these meter guys are under pressure to fit certain number of meters per day. They don't waste time poking around the consumers side or looking for defects with the exception of gas leaks.
 
Well to be fair these meter guys are under pressure to fit certain number of meters per day. They don't waste time poking around the consumers side or looking for defects with the exception of gas leaks.

They have to fill in what I think is called a MOPs report which is a meter operators sheet where they note any defects or queries to the existing equipment. They waste a lot of DNO time reporting exposed conductive parts in the cutout, what the rest of us would call the pme terminal. Each report has to be investigated.
 
This used to be economy 7 where the CUs are remote from the meter box and so require KMFs due to distance.
The bottom one was for the off peak which has become obsolete probably due to gas central heating replacing electric storage heating.
That is a British Gas smart meter and electric is not their strong point.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Andy5678

Arms
~
Joined
Location
Scotland
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
What would you do here.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Thread Tags

Advert

Thread statistics

Created
Andy5678,
Last reply from
Graham DJ,
Replies
19
Views
2,509

Advert