New member and DIY. I have a 60 AMP breaker going to a sub panel for a workshop. Two months ago I bought an electric car and a 40 AMP charger that I wired a 50 AMP breaker to my sub panel.

I charge from midnight to 7 am and everything has been fine for 2 months. Last night the main 60 AMP breaker popped several times after resetting it but the 50 AMP which is directly wired to the charger did not.

My charger allows me to adjust the output and I lowered it from 40 to 30 amps and it popped again. I then lowered it to 20 AMPS and it did not pop again.

Can anyone give me a clue as to why the 60 AMP breaker popped. The only thing running on the sub panel was the charger.

Thanks very much for any help. Ken.
 
I would change the old 60A breaker for a new one, if the problem persists then you have a fault that needs investigating, do not keep resetting it.
if the problem goes away then it is reasonable to assume the breaker was faulty.
 
Yes, I have a worshop but all tools and lights were off. I even turned the new breakers off of everything except the charger and it still popped.
That brings it down to one (or worst case more) of:
  • The 60A breaker is faulty
  • The cable run has a fault
  • The charger has a fault
Altering the charge setting appears to stop it, so cable is less likely, and I suspect a replacement breaker is the cheapest test to rule that out before you consider the expensive case of a faulty charger.

Just to check this is over current only simple breaker, not a GFCI/RCBO unit?
 
That brings it down to one (or worst case more) of:
  • The 60A breaker is faulty
  • The cable run has a fault
  • The charger has a fault
Altering the charge setting appears to stop it, so cable is less likely, and I suspect a replacement breaker is the cheapest test to rule that out before you consider the expensive case of a faulty charger.

Just to check this is over current only simple breaker, not a GFCI/RCBO unit?
Thanks very much for your reply. I installed
a new breaker and it appears to have fixed the problem since I charged at 40 amps last night with no problem.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Dallas GA
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United States of America
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
Why did 60 Amp breaker pop
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
7
Unsolved
--

Advert

Thread statistics

Created
Kenewber,
Last reply from
Kenewber,
Replies
7
Views
1,690

Advert

Back
Top