Do I need to install a small CU to provide 3no separate supplies to 3 no ovens from the single 32amp supply I currently have.
 
  • Optimistic
Reactions: DPG
Watt is the kw for the ovens ?;) are you a member boys band ?
 
  • Like
Reactions: DPG
Yes, the detail is a bit sparse here.
 
You don't necessarily need to provide a separate OCPD for each appliance as long as fault protection is OK for the tail to each appliance. Also check manufacturers instructions in case they specify a fuse size,which regardless of how pointless it seems you will have to comply with. Otherwise I would just link the incoming 6,0mm(?) between 3x 20a DP isolators,MK (for example) 20a isolators will take 2x 6.0mm conductors, because I have terminated them in the past. Or you could use 32a isolators if you prefer. 45mm deep back boxes will be a good idea, 35 will be tight....don't even think about 25mm
 
  • Like
Reactions: 123 and Rpa07

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Wiring 3no 3.2kw 16amp ovens to an existing 32amp 6mm supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
5

Advert

Thread statistics

Created
Patrick Boyle,
Last reply from
Deleted member 9648,
Replies
5
Views
1,379

Advert