Hi all just a quick question. Understand how to carry out both tests and what the right reading ie max reading should be, but what wouLd you do if the reading you receive is to high.
Ze do you contact the electrical board?
And zs what would be the options?
Thanks once again
Chris
Ze do you contact the electrical board? only if it's a TN system
And zs what would be the options? rewire circuit in larger cable, fit a lower rated MCB,
Thanks once again
Chris
my comments in red
Thanks once again
Chris
If it's a TN (S/C-S) then contact the DNO to rectify (or the may say it's ok, depending on what reading it is).
If it's a TT system then you'll need to try and get the reading down.
Assuming the above are ok, then for Zs, assuming your r1 and r2 are ok (and R1+R2 is ok), either break down into separate circuits or use larger cable etc
So for instance if i got a ZE of 0.07 and a PFC of 3.5 KA on a 30 A BS3036, what would I need to do then? Especially if budget is at almost zero? Install rcd isolator on the tails?
Depends on what the suppliers fuse is in that case. The BS3036's are normally rated to 2KA max, so you are then reliant on the suppliers fuse, so probably ok. What's rcd protection got to do with this? Are you suggsting installing that to overcome the breaking limit on the BS3036's?
I got that impression from Marniks post someone could do that. I'm getting a bit confused. So the only way to overcome the problem would be to change the DB then? RCD is only for residual current not over current.
oops :6:
That the PFC at 3.5 KA is too high for the BS3036 30A Fuses.
Problem is that I have fed a 2X 32A RCBO's from the 2X BS3036 30A fuse so that the Ring main and new load cable for the cooker circuit I have added to is compliant. Some of the cables are in plastic oval at a depth less than 50mm so therefore require RCD protection.
So I put in a 4 way fuse board with just the 2 RCBO's in.
Also there fore the installation still has one point of isolation.
You're covered by the suppliers fuse for breaking capacity, so the problem you've to overcome is the lack of RCD protection for the cable.
to be continued in a new post ....
Reply to Ze and zs testing! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Fluke MultiFunction Tester 1662 TNS Earthing system. Switchboard - 415v - 3 Phase + Neutral + Earth. MCB 1000A 3 individual Earths (185mm)...
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Evening everyone, I was taught when carrying out Zs testing to test both L-PE and L-N and record the highest result of the two tests for my Zs...
Evening everyone . I was changing a fuse board today . Everything tested out fine and good . Until I measured the Ze which is on a tnc-s system...