Zs=Ze+R1+R2 if you have R1+R2 and the Ze of cu through dead testing what is the need of doing an earth fault loop impedance test once you've energised the cu?
 
Ok so along as you have Ze of cu and R1+R2 no need for earth loop? As you can work out Zs
 
Yes but I've got a feeling this could be a long thread. That's 101 of testing.

And I'll correct myself. 'R2'
 
My 20p : Testing the earth fault loop confirms it actually works, and the value obtained can be cross checked with the expected values from design and Ze etc.
 
by measurement or
by enquiry from the dno
or calculation
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
London
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
Zs,Ze,R1+R2
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
9

Advert

Thread statistics

Created
Bradley6969,
Last reply from
Wilko,
Replies
9
Views
2,044

Advert