OP
snowplough
Sorry push should read what i write,
I started off saying that i would never have thought you can obtain parrallel path readings by using the test method two with croc clip on earth bar on a R1+R2 dead test, which would give you a lower reading .
Then i was thinking well it might be an incorrect R1+R2 measured reading by not disconnecting the cpc from earth at test, but does it really matter when overall, it can only contribute to a lower Zs reading, which means disconnection times can be met, lowering the electric shock risk.
Many Thanks
lOCKET
I started off saying that i would never have thought you can obtain parrallel path readings by using the test method two with croc clip on earth bar on a R1+R2 dead test, which would give you a lower reading .
Then i was thinking well it might be an incorrect R1+R2 measured reading by not disconnecting the cpc from earth at test, but does it really matter when overall, it can only contribute to a lower Zs reading, which means disconnection times can be met, lowering the electric shock risk.
Many Thanks
lOCKET