carrying out an eicr in a church, and just wanting some clarification regarding r2 readings on heating pipework throughout the building?

thanks in advance!
 
Morning all!

carrying out an eicr in a church, and just wanting some clarification regarding r2 readings on heating pipework throughout the building?

thanks in advance!


Not sure what you mean r2 readings, are you trying to find out if the rads require bonding?
 
Morning all!

carrying out an eicr in a church, and just wanting some clarification regarding r2 readings on heating pipework throughout the building?

thanks in advance!

I suppose you mean R2, as r2 is what you would measure when carrying out end to end on a RFC. :smile:

Your question lacks some info to be honest. Are these pipes extraneous?
 
  • Like
Reactions: 1 person
I suppose you mean R2, as r2 is what you would measure when carrying out end to end on a RFC. :smile:

Your question lacks some info to be honest. Are these pipes extraneous?


Think that is what the op is trying to find out although I have been known to be wrong
 
Sorry for the lack of info.....

i have done R2 readings on various pipes and rads around the building, and have been getting readings up to 0.83 ohms, when I'd have been expecting much lower.

In view of the fact that you don't test every pipe around a house, and this is just a 'big house' what is the general consensus?
 
A the reading is not that low, but low enough to be extraneous, I think maybe some more investigation is required?
 
readings up to 0.83 ohms, when I'd have been expecting much lower.

Why are you expecting much lower?

What is the length and resistivity of the copper pipe?

Have you nulled your meter leads/wander lead?
 
Last edited:
Why are you expecting much lower?

What is the length and resistivity of the copper pipe?

Have you nulled your meter leads/wander lead?

I think I'm getting mixed up with expecting readings in line with main bonding continuity readings?

I have no idea!

Yes, I have.
 
I think I'm getting mixed up with expecting readings in line with main bonding continuity readings?

I have no idea!

Yes, I have.

And what reading would you expect on main bonding continuity then?

I think your second point sums it up nicely
 
  • Like
Reactions: 1 person
Sorry for the lack of info.....

i have done R2 readings on various pipes and rads around the building, and have been getting readings up to 0.83 ohms, when I'd have been expecting much lower.

In view of the fact that you don't test every pipe around a house, and this is just a 'big house' what is the general consensus?

It's not really just a big house, it's more normally a large open space where a large number of members of the general public can be expected to be which is often a listed historical building and with an increased fire risk.
 
Could be really old iron pipework and probably rusted to an extent on the threaded joints too. All assumptions of course but in my mind the readings are fine.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread Information

Title
Bonding of rads in a church
Prefix
N/A
Forum
Periodic Inspection Reporting & Certification
Start date
Last reply date
Replies
14

Thread Tags

Advert

Thread statistics

Created
maffa ent,
Last reply from
Dave OCD,
Replies
14
Views
2,216

Advert