I have found that the inverter is capable of tripping a maximum of 16A B type MCB under overload conditions, anything of a higher rating requires an rcd for fault protection.

How quickly does it trip it and at what current? Just saying it can trip an mcb under overload could be very different to fault conditions.

An RCD will not work without one pile of the supply being referenced to earth, otherwise you have two floating poles with no earth reference and nothing for the RCD to work from
 
How quickly does it trip it and at what current? Just saying it can trip an mcb under overload could be very different to fault conditions.

An RCD will not work without one pile of the supply being referenced to earth, otherwise you have two floating poles with no earth reference and nothing for the RCD to work from


It trips in the desired times now that it is connected to the rcd side of the installation and the installation is referenced to earth through a rod (TT) the manual for the solar installation requires that it be installed with a TT earthing arrangement.

The equipment is supplied by SMA if you'd like to take look in to it.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Sub Main MCB supply cable
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
21

Advert

Thread statistics

Created
Pmarsh,
Last reply from
Pmarsh,
Replies
21
Views
4,184

Advert