Hi - My first post to this forum.

I am having a disagreement with another electrician on the type of the supply characteristics for a domestic installation, i.e. whether it is TN-S or TN-C-S. I have uploaded a photo of the cutout/supply head. To resolve the disagreement I suggested we ask for a 3rd, 4th, 5th .... opinion from the forum.

The building is in a suburban area and is over 100 years old , not that I am suggesting that the supply head is that old. There are no PME labels/markings. The measured Ze is 0.11 ohms.

Thanks for your views in advance.

jlrb

Supply Type.jpg
 
only DNO could tell you for sure . rare to see supply in split concentric.
 
  • Dislike
Reactions: 1 person
measure both pefc and pscc. if they are the same, i'd opt for TNC-S.
 
  • Agree
Reactions: static zap
measure both pefc and pscc. if they are the same, i'd opt for TNC-S.

Thanks - that was my thought on next step too if there isn't a barrage of consensus from the forum. Even then it will still be an inferred result which I was hoping to avoid.
 
you could always dig up the supply cable and see where the earth is. :(
 
  • Funny
Reactions: 1 person
Did you test L-N fault loop?

measure both pefc and pscc. if they are the same, i'd opt for TNC-S.

As Murdoch and telectrix suggested:

Measured PEFC = 2.10 kA (0.11 ohms)
Measured PSSC = 1.30 kA (0.18 ohms)

This indicates to me that it is TN-S rather than TN-C-S, but I was expecting the relative values to be the other way around - but on reflection I am not sure why I should expect that.
 
Surely it must be TN-S as there appears to be a separate neutral and protective conductor. As there is no PEN conductor it can't be TN-C-S.

It's also in a bloody dangerous condition!
 
Hi,
1. Why did you open the head? You have no right to do so and the older ones can and do go bang. (research arc flash).
2. When you did the the PEFC test did you isolate the installation, disconnect the earth cable from the terminal shown and test at that terminal?
 
The neutral and cpc are not combined so TN-S.
 
  • Agree
Reactions: 1 person

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Advert

Thread statistics

Created
jlrb,
Last reply from
Lee42,
Replies
35
Views
3,845

Advert