Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.

Supply to property TN-C-S

Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)

Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.

Earth rod with 10mm to the RCD spur and TT the rest.

Any advice would be great
 
What rating is the hot tub?
I usually do away with fcu option and just keep it all at 16amp..
obviously still have RCD protection
 
Isolator switch required close to the hot tub.
 
  • Agree
Reactions: robd
4mm - 13A???

Earth rod - why?

I would fit a socket if the customer is having a hot tub company deliver it as they will only want to see a socket.

I’ve had a few call outs where they have used a standard plug & socket, couldn’t remove the plug as it had melted onto the socket..

One of them shouldn’t have been on a 13a plug, as it was rated at about 3.2 kw.
The hire company had used a commando plug to 13a converter
 
Hi, I've been asked to install 13amp supply for a hot tub around 30m from the house.

Supply to property TN-C-S

Plan is to run a 4mm 2 core swa from a 16 amp mcb in the CU to a IP66 RCD switched fused spur (Aprox 25m from house)

Use the armour as the earth until it reaches the Rcd spur in which case I will heat shrink swa and then fit stuffing gland to terminate.

Earth rod with 10mm to the RCD spur and TT the rest.

Any advice would be great
Heat shrink the SWA? I take it you mean connect the armour to the Earth terminal in the FCU? Advice use a banjo on the SWA and use some suitably sized wire from there to the terminal, If I read your intentions correctly that is not the way to install this SWA, have you done any calculation for cable sizing. or is this a stab in the dark job. a stuffing gland is not the correct method, well you did ask.
 
  • Agree
Reactions: Deleted account
The reason for heat shrink was to drop the pme earth at the FCU

As in the regs it recommends not to use PME earth.
 
For give me if I'm wrong on the earthing arangement.

I have around 80m of 4mm swa in my garage that needs using up should have stated that in original post.

I'm going to have to ring up the hot tub company as it only say on there website 13amp supply. Could really do with a power spec
 
  • Agree
Reactions: Deleted account
For that length of run you will need 6mm, based on a load towards the maximum 13 amp.
If you really want to use the 4mm then you will need to double up the cores
 
For these plug in hot tubs, Is there a minimum distance the socket must be from the side of the hot tub, obviously zones apply, is it the same as a bath,
 
Isolator switch required close to the hot tub.

Is an isolator still required with 13a plug and socket hot tubs?,
obviously with the 32a they would be
 
For that length of run you will need 6mm, based on a load towards the maximum 13 amp.
If you really want to use the 4mm then you will need to double up the cores

You sure about that? 16amp supply 4mm is about 60meters off the top of my head

I may be wrong
 
For that length of run you will need 6mm, based on a load towards the maximum 13 amp.
If you really want to use the 4mm then you will need to double up the cores

You sure about that? 16amp supply 4mm is about 60meters off the top of my head
 
you will probably find out from the tub supplier/manufacturer that it come with an integrated 10mA RCD in the mains lead. i get the VD on 4.0mm to be 4.3V so it's adequate for the job. ( 11 x 13 x 30 )/1000.
 
Would you drop the pme earth at socket/isolator and TT the rest or am I over thinking it ?
 
Would you drop the pme earth at socket/isolator and TT the rest or am I over thinking it ?
I’ve read here before now, that some would do both.

What surface is the hot tub being installed on?
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
13amp Hot tub supply
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
57

Advert

Thread statistics

Created
HRM-ELEC,
Last reply from
UNG,
Replies
57
Views
7,434

Advert