This is a new one on me and not so sure how to tackle it. The customer is extending 3 bedrooms, ive quoted to install new lighting circuit for these rooms.

The existing circuit for the upstairs lighting does not have an earth and due to its routing it will need extending to fit round the shape of the new rooms. This existing circuit is supplying j.b's in the loft that spider to the bathroom, hall, and another bedroom; the customer will not agree to have these rooms rewired in t&e as it means making holes in the ceilings ! (----)

If I bring in a new feed to the existing J'bs how do I stand on reconnecting the existing circuits that dont have a cpc ?? Customer is adamant he dont want existing rewired but he wants the lights back on, I will IR each of these existing lighting circuits, if they pass I was thinking to make a note on the EIC that customer refuses rewire, and then reconnect.
 
just put a new circuit to new area ,on the test cert put existing circuit needs rewire ,the end.
 
  • Agree
Reactions: Strima and Andy78
just put a new circuit to new area ,on the test cert put existing circuit needs rewire ,the end.

Yeh Buzz that would be functional but aint there a caveat in the regs that a new circuit should be sound "all the way round" so to speak.
[automerge]1568146967[/automerge]
just put a new circuit to new area ,on the test cert put existing circuit needs rewire ,the end.

Just re-read that, yeh I see what you mean. If the customer don't agree to rewire then can I do what I said in original post, thanks.
 
  • Like
Reactions: buzzlightyear
you can not put gun to a customers head if they dont want it done .when you quote for a job tell them what you are going to do.
 
  • Like
Reactions: Deleted account
Agree with Buzz. All your work must be compliant so a new circuit for your work would be the best way. Cite 132.16 to back yourself up.
Also tell them their 50+ year old wiring is due for a rewire when they get round to it.
 
Also tell them their 50+ year old wiring is due for a rewire when they get round to it
when the most of the house burns down and the extension still standing,lol.
 
Make sure they don’t want any metal switches or fittings on their unearthed lighting circuits
 
Ive really recommended a rewire of existing lighting and switch drops but he's not having it full stop, don't know why but hes a problem customer who wont listen. Anyway the existing feed to the loft needs extending to get the lights back on as the builder cut the cable when he demolished the bedrooms. I was not certain on reconnecting this to the existing lights and switches that don't have an earth. Once ive convinced myself what to do I will get customer to sign a disclaimer and reconnect. The circuit is rcd'd and all class 2 at least.
 
  • Like
Reactions: buzzlightyear
Ive really recommended a rewire of existing lighting and switch drops but he's not having it full stop, don't know why but hes a problem customer who wont listen. Anyway the existing feed to the loft needs extending to get the lights back on as the builder cut the cable when he demolished the bedrooms. I was not certain on reconnecting this to the existing lights and switches that don't have an earth. Once ive convinced myself what to do I will get customer to sign a disclaimer and reconnect. The circuit is rcd'd and all class 2 at least.
Might be one worth swerving if they already a problem.
 
This is a new one on me and not so sure how to tackle it. The customer is extending 3 bedrooms, ive quoted to install new lighting circuit for these rooms.

The existing circuit for the upstairs lighting does not have an earth and due to its routing it will need extending to fit round the shape of the new rooms. This existing circuit is supplying j.b's in the loft that spider to the bathroom, hall, and another bedroom; the customer will not agree to have these rooms rewired in t&e as it means making holes in the ceilings ! (----)

If I bring in a new feed to the existing J'bs how do I stand on reconnecting the existing circuits that dont have a cpc ?? Customer is adamant he dont want existing rewired but he wants the lights back on, I will IR each of these existing lighting circuits, if they pass I was thinking to make a note on the EIC that customer refuses rewire, and then reconnect.
Baptism if they keep acting like that give them a ridiculous price and see if they go for it and tell them you have rules you have to go by. If that doesn’t do it walk away
 
Ive really recommended a rewire of existing lighting and switch drops but he's not having it full stop, don't know why but hes a problem customer who wont listen. Anyway the existing feed to the loft needs extending to get the lights back on as the builder cut the cable when he demolished the bedrooms. I was not certain on reconnecting this to the existing lights and switches that don't have an earth. Once ive convinced myself what to do I will get customer to sign a disclaimer and reconnect. The circuit is rcd'd and all class 2 at least.
Give quote to do what you feel is right. If he doesn’t agree walk away.

EDIT: beat me to it megawatt
 
  • Like
Reactions: Megawatt
I was not certain on reconnecting this to the existing lights and switches that don't have an earth
me I would tell the builder to get his own spark in to reconnect .are you working for the builder or the customer ?.
 
For the customer
tell the customer that the builder to sort what needs reconnecting .you are going to contract to the customer not the builder, if not walk.
 
  • Like
Reactions: Megawatt
The absence of a cpc means ADS is not complied with and this part of the installation is not Class II no matter what accessories are fitted as general purpose accessories are not Class II. The inclusion of an rcd is irrelevant. A disclaimer would hold little water as your client is probably signing something to which he/she has no understanding of.
 
The absence of a cpc means ADS is not complied with and this part of the installation is not Class II no matter what accessories are fitted as general purpose accessories are not Class II. The inclusion of an rcd is irrelevant. A disclaimer would hold little water as your client is probably signing something to which he/she has no understanding of.

Thanks for the info, although that part of the installation I will not touch. Im concerned with running a new supply (which will have a cpc) to the existing lighting jb which serves the existing lights and switches. Is this recommended or not was the reason for the post.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Lighting circuit what to do
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
57

Advert

Thread statistics

Created
haptism,
Last reply from
Haworth,
Replies
57
Views
7,421

Advert