TheCodboy
371
128
118
Newcastle
Hi all, looking for a bit of advice and confirmation on my proposed plans for a SWA sub main to a ISO metal storage container. I've calculated the max demand in the ISO will be about 20A (300w of led lighting and 2 double sockets for chargers etc) It will be fed from a 3ph DB in another building. The cable run is 100 meters, I'm planning on using 16mm 2 core swa ( Volt drop calcs allow about 35A with 16mm) and installing a rod at the container (the vast majority of the cable run is at height, clipped to the building). The container will have a small 4 way board with RCD main switch.
The 16mm will be fed from a C32 breaker in the 3Ph board. Im installing double insulated 16mm tails and a 16mm earth from the 3ph DB to a meter (needs a meter installed) then from the meter to an adaptable box where I will terminate the SWA. Due to the fact that I'm using a rod at the other end, I'm planning on a 100ma S rcd for fault protection for the SWA (inside the adaptable box).
Can anybody see any glaring errors in my method? I have spoke to Napit and they were fine about my proposed plan, but they didn't mention the 100mA rcd.
Thanks in advance!
Looks fine to me crack on.
Why the need for a 100ma rcd assuming the type C device will provide fault protection.
It's an old Square D board and there a few spare 32's in the board. Thought I'd utilise that rather than trying to source another MCB.
Why the 100ma rcd.
Reactions: buzzlightyear
How is the SWA cable going in?
Would I not need the 100mA due to the Zdb being higher than the permissible Zs value for disconnection with the C32 mcb
So the C32 wouldn't provide fault protection.
Now we have established what you are doing draw us a plan from start to end. If possible.
What is the Zs/Ze of the supply board?
If you go with 16mm 2-core then you have R1+R2 = 1.15 + 3.7 = 4.85 ohm/km so 0.485 ohm and for a C32 MCB you would need no more than 0.55 ohm end of circuit Zs so supply Ze has to be 0.06 ohm or less. Unlikely.
Your VD limit would be met for 10mm, so going 3-core there your R1+R2 is 1.83 + 1.83 (ignoring armour's 6.0 in parallel for now) = 0.366 for 100m so Ze <= 0.18 ohm, which is possible.
Is this a TN-C-S supply? If so the 16mm 2-core will not meet the 10mm copper equivalent for bonding an extraneous part (armour is 42mm steel, so about 5.3mm copper equivalent), so either it has to be TT'd or you go for 10mm 3-core.
If using the 100mA RCD for avoidance of sane limits on supply Ze it will have to be at the source end, so a cable fault still meets 5s or less disconnection, and ideally a delay one so it has selectivity with the 30mA RCD for the socket outlets. No one is going to be happy walking 200m round trip to reset it!
Other options for Ze avoidance would be a 32A switched-fuse as then you would meet 5s disconnection on 1.25 ohm end-of-circuit Zs (OSG Table B4), but obviously no selectivity with the 32A C MCB, and probably little with the socket circuits (probably fine for post-13A fuse fault, not so one a 20A B RCBO or whatever and fixed wiring fault).
Your VD limit would be met for 10mm, so going 3-core there your R1+R2 is 1.83 + 1.83 (ignoring armour in parallel for now) = 0.366 for 100m so Ze <= 0.18 ohm, which is possible.
Other options for Ze avoidance would be a 32A switched-fuse as then you would meet disconnection on 1.25 ohm end-of-circuit Zs, but obviously no selectivity with the 32A C MCB, and probably little with the socket circuits (probably fine for post-13A fuse, not so one a 20A B RCBO or whatever).
It will be TT
Reactions: pc1966
It will be TT
OK, so you just need to meet the SWA fault protection so RCD up-front on basically any SWA choice, and a rod arrangement below 200 ohms. What is the surrounding soil/ground like?