Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
 
Client wants 2g socket in greenhouse, obviously IP rated,will be supplied from Rcd, the greenhouse consists of metal frame work on the ground.
Does this require MPBC
I would say so because the metal frame does represent an extraneous conductive part. (411.3.1.2 item v)

At least now the bonding doesn't have to be 10mm^2
 
Last edited:
  • Like
Reactions: loz2754
I would say so because the metal frame does represent an extraneous conductive part.

At least now the bonding doesn't have to be 10mm^2
With that in mind that Power point will need its own earthing system ie:TT
 
  • Like
Reactions: timhoward and DPG
What with & where from, its either MPBC or supplementary

Neither, the equivalent of MPBC as detailed in 544.1.1

So 6mm^2
 
  • Like
Reactions: timhoward
Which is 10mm from a Tncs supply.
Why, what size cable are you taking to the glass house???

If you take 6mm^2 then that would meet the minimum x section.

Use the CPC of 6mm^2 as bonding for the seperate building.
 
Deemed as a Special location this Power Point now becomes an expensive item.
To comply it will need a TT earthing system for the greenhouse to accommodate MPBC
 
Deemed as a Special location this Power Point now becomes an expensive item.
To comply it will need a TT earthing system for the greenhouse to accommodate MPBC

Why?
 
Why, what size cable are you taking to the glass house???

If you take 6mm^2 then that would meet the minimum x section.

Use the CPC of 6mm^2 as bonding for the seperate building.
It‘s a 2.5mm from local ring main
The MPBC size relates to the existing earthing system isnt it
 
It‘s a 2.5mm from local ring main
The MPBC size relates to the existing earthing system isnt it

No, it's not the MPBC, it's extraneous conductive part in a remote building therefore the bonding size is dependent upon the circuit to that building.
 
The key part is the second paragraph:

"Where an installation covers more than one building, a main protective bonding conductor shall be selected in accordance with the characteristic of the distribution circuit protective conductor for that particular building."



(Min 6mm^2; max needed 25mm^2 of course)
 
Agree to disagree here, you say use the cpc of the 6.0mm for the bonding, cpc & bonding are 2 different functions.
 
Agree to disagree here, you say use the cpc of the 6.0mm for the bonding, cpc & bonding are 2 different functions.

You can use the cpc for the supply to the remote building as both a cpc for that sub board and bonding provided it meets the minimum cross section for both aspects.

You could use 2.5mm^2 for the circuit, but as it wouldn't meet the minimum for bonding, would require an additional 6mm^2 for bonding; or use a 6mm^2 combined circuit and bonding conductor.

Edit

Third choice would be a 2.5 or 4mm^2 - 3 core swa, which combined with the swa armour would give a combined x section greater than 6mm^2

Haven't got tables to hand, but pretty sure both sizes will give more than 6mm^2 combined.

Edit 2:

Even a 2 core 1.5mm^2 swa has an armour of 15mm^2 so would actually be ok for both the CPC and bonding (though I prefer 3 core for a "proper" cpc)
 
Last edited:
The key part is the second paragraph:

"Where an installation covers more than one building, a main protective bonding conductor shall be selected in accordance with the characteristic of the distribution circuit protective conductor for that particular building."



(Min 6mm^2; max needed 25mm^2 of course)
You can use the cpc for the supply to the remote building as both a cpc for that sub board and bonding provided it meets the minimum cross section for both aspects.

You could use 2.5mm^2 for the circuit, but as it wouldn't meet the minimum for bonding, would require an additional 6mm^2 for bonding; or use a 6mm^2 combined circuit and bonding conductor.
In many cases we’ve been told that supplying a remote garage from a Tncs supply a 10mm bonding must be installed if there are extraneous conductive parts in that area.
In many cases the easiest option would be to convert to a TT System & install a 6.0 mm
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

cliffed

Arms
~
Joined
Location
Worcester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Power point in external glasshouse
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
99

Advert

Thread statistics

Created
cliffed,
Last reply from
pc1966,
Replies
99
Views
8,339

Advert